what is advantage of using star to delta in place of dol
starter
Answers were Sorted based on User's Feedback
Answer / srilu
decrease starting current by 1/3 times of rated current to
avoid burning of motor during starting
Is This Answer Correct ? | 12 Yes | 1 No |
When the supply voltage is lower than the rated voltage we generally use star delta starter to avoid the over load trip. But in DOL starter, supply rated supply voltage need to start the load
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / liliosa b
it is cheaper compared to other reduced voltage methods
Is This Answer Correct ? | 0 Yes | 1 No |