I have 3KVA Libert GTX2 UPS. I need to calculate the back
up time with some load. How to calculate the Back time. I
need the expert guide
Answer Posted / k.prakashchandra
The energy stored in each battery is = voltage of the
battery x AH of the battery in watt hour.If you multiply
this with the number of batteries ,you will arrive at total
energy stored in watt hour.This when divided by the load in
watts will give you back up time in hours.This method holds
good for both series and parallel connections of batteries .
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
What is conventional thermal current (Ith)
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
An ISP is granted a block of addresses starting with 150.80.0.0/16. The ISP wants to distribute these blocks to 2600 customers as follows. a) 200 medium size businesses; each needs 16 addresses b) 400 small businesses; each needs 8 addresses c) 2000 households; each needs 4 addresses Design the subblocks and give the slash notation for each subblock. Find out how many addresses are still available after these allocations.
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
what can be the causes of capacitor start motor having a higher current that its actual
why we change the direction of winding in rotor ?how we make the north and south pole?
For the requirement of a furnace of temperature range up to 1200 oC using silicon carbide rods, What is the required rate of transformer needed (please do it with all details)?
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
for opening electrical shop, tips needed.
What can you contribute to the progress of our Company as an employee if you are selected?
What is different between Difnit time and instatous over current relay
different aspects of voltage stability