what is the range of using dol starter & star delta
starter.
Answers were Sorted based on User's Feedback
Answer / venkatesh sk
below 5hp motor used dol 5to 15hp motor used stardelta
starer
Is This Answer Correct ? | 114 Yes | 21 No |
Answer / pawan dahiya
DOL using gange normal used 5HP and 5HP to above used in
star delta. Because 5 HP above value without star delta
motor/pumps starting time requied power(yani three gunaa
reating ki)
Is This Answer Correct ? | 38 Yes | 3 No |
Answer / prakash suhane
There is no hard N fast rule which state the range of star
delta and DOL starter, we have to keep in mind fallowing
points during configuration of DOL starter.
1) Motor should not be of very high rating.
2) Starting torque (reqd to start motor)is not very high.
apart from above case we should use star delta starter.
Is This Answer Correct ? | 25 Yes | 6 No |
Answer / nani
Now a days we are using DOL starter up to 3ooKw, it can
possible, already we are working in this system.
Is This Answer Correct ? | 23 Yes | 10 No |
Answer / pawan dahiya
Normal Dol Rang less then 5 HP and Star Delta Used Normal
5 HP to 15HP
Is This Answer Correct ? | 16 Yes | 7 No |
Answer / rajkumar saini
below 5 hp using DOL starter & above 5HP using star delta
starter
Is This Answer Correct ? | 13 Yes | 7 No |
Answer / bikash bhagat
the range of using dol starter is under 5 hp & above 5 hp we can use star delta starter because when we start the motor the starting current is inreases 5 to 7 times than the rated motor full load current so it should effected the motor thats why above 5 hp we use star delta starter
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / rangaraj
dol starter is us 5hp motor(3.5kw)in direct current.star delta starter is us above 7.5hp starting current high in star and delta delta reduced 3-4 times voltage.dol connection star and delta connection delta.... rangaraj015@gmail.com
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pawan
Till 5HP motors we use DOL starters . If we use beyond it,there will be a drip in the mains power supply.. Beyond 5HP, star delta is use as firstly motor operate in delta and thus its starting voltage is less(which is req. as in starting no back emf is there) after an instant it start operating in star as now motor has developed sufficient back emf to counter the voltage. Now the current is less(I/root3) as less current is beneficial reducing losses.. Now the ques. arises why only 5HP?Why not 5.2 or 5.5? The answer is its just a standard value.When it is tested beyond 5HP, drip is showing.. Thus the value 5HP.. Also motor are not available as 5.2 or 5.3 HP..So the standard value taken is 5HP...
Is This Answer Correct ? | 2 Yes | 4 No |
what are the values of VRY,VYB,VBR,Vry,Vyb,Vbr,Vrn,Vyn,Vbn for Magenetic balance test of 100 KVA and 63 KVA Distribution transformer
Why reverse power relay is used?
How to select the rating of a CT used for REF protection. The rating can be of equal rating of Phase current or neutral current rating
why phase to phase voltage are 290 rather then 440?
what is auxilliary transformer??
What happens when the field of an alternator connected to infinite bus is suddenly removed?
why we use star connection in HT motor? and delta connection in LT motor
why current is denoted by I
What is phase cross over frequency?
what are the different pre- commissioning tests performed on distribution transformer, power cable and switchgear?????
why transformers are put with supply for 24 hours before giving supplying to a locality?
What is Goerges phenomina to start SYCHNOUSMOTOR?