what is the range of using dol starter & star delta
starter.
Answers were Sorted based on User's Feedback
Answer / venkatesh sk
below 5hp motor used dol 5to 15hp motor used stardelta
starer
| Is This Answer Correct ? | 114 Yes | 21 No |
Answer / pawan dahiya
DOL using gange normal used 5HP and 5HP to above used in
star delta. Because 5 HP above value without star delta
motor/pumps starting time requied power(yani three gunaa
reating ki)
| Is This Answer Correct ? | 38 Yes | 3 No |
Answer / prakash suhane
There is no hard N fast rule which state the range of star
delta and DOL starter, we have to keep in mind fallowing
points during configuration of DOL starter.
1) Motor should not be of very high rating.
2) Starting torque (reqd to start motor)is not very high.
apart from above case we should use star delta starter.
| Is This Answer Correct ? | 25 Yes | 6 No |
Answer / nani
Now a days we are using DOL starter up to 3ooKw, it can
possible, already we are working in this system.
| Is This Answer Correct ? | 23 Yes | 10 No |
Answer / pawan dahiya
Normal Dol Rang less then 5 HP and Star Delta Used Normal
5 HP to 15HP
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / rajkumar saini
below 5 hp using DOL starter & above 5HP using star delta
starter
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / bikash bhagat
the range of using dol starter is under 5 hp & above 5 hp we can use star delta starter because when we start the motor the starting current is inreases 5 to 7 times than the rated motor full load current so it should effected the motor thats why above 5 hp we use star delta starter
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / rangaraj
dol starter is us 5hp motor(3.5kw)in direct current.star delta starter is us above 7.5hp starting current high in star and delta delta reduced 3-4 times voltage.dol connection star and delta connection delta.... rangaraj015@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pawan
Till 5HP motors we use DOL starters . If we use beyond it,there will be a drip in the mains power supply.. Beyond 5HP, star delta is use as firstly motor operate in delta and thus its starting voltage is less(which is req. as in starting no back emf is there) after an instant it start operating in star as now motor has developed sufficient back emf to counter the voltage. Now the current is less(I/root3) as less current is beneficial reducing losses.. Now the ques. arises why only 5HP?Why not 5.2 or 5.5? The answer is its just a standard value.When it is tested beyond 5HP, drip is showing.. Thus the value 5HP.. Also motor are not available as 5.2 or 5.3 HP..So the standard value taken is 5HP...
| Is This Answer Correct ? | 2 Yes | 4 No |
iam working as a electrical engineer. i want to know about any license or certificates regarding my field. for my carrier and ti improve the knoweledge.,,, how we get that..and what procedures......... pls help me
How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set required to cater to this load?
3 Answers Bhel, INDUS, Indus Towers,
In chillers & freezers which gas will be use?
What does substation operator do in substation?
What is Tachometer used to measure?
What is the difference between reverse power trip & inadvertant trip?
Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable
as ac supply is given 2 the transformer why it doesnot depends upon powerfactor????
I want Primary side delta and Sec side Star connection transformer . but i have received Star - Star transformer ,shall i use the same transformer by giving the only 3 ph on Primary side without Neutral connection on the Starpoint.
why DG sets power factor is 0.8 lagging.
what is GRR(Grid Rotot resistance)?Why it is used beside of LRS?
9 Answers ACC, L&T, Sri Biotech,
what is the difference between high impedance and low impedance circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)