whats was the problem if neutral and earth got 2volt from
the ups output
Answer / b.dhanasekaran
no problem, but you strengthen the earth value to 1 ohm,
and cheque the load connections if there is loose
connection in neutral.
| Is This Answer Correct ? | 3 Yes | 0 No |
briefly explain principle of resistance welding
why the armature coil in dc machine is round?? swagat k.
why auto transformer connected in star?
What is power in wattage of 8.5 TR AC
how much test voltage should applied for tan delta test.
What do you mean by per capita requirement of electrical energy in india
how to reduce earth resistance in sandy soil.
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
why transformer donot allow the dc?
what is rating providing of contactor,relay,fuse unit for motor output power
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
how to calculate the formula of cable size if motor kw is given
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)