why neutral should connect to earth in delta-star type
transformer
Answers were Sorted based on User's Feedback
Answer / ravi
To keep the neutral stable in case of unbalanced loads, to
nullify the 3rd harmonic currents in the windings by
carrying to them to ground
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / sinod kumar
to provide a path for odd harmonics(mainly 3rd &
5th)component of magnetizing current to get sinusoidal flux
and undistorted emf.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kartikesh
To provide a path to ground to winding harmonic rrent
generated due to unbalanced load ,to nulified the 3rd
hamonic current it should be grounded
| Is This Answer Correct ? | 0 Yes | 0 No |
if name plate detals of a motor or any other is missing then how to find it
how induction generator works?
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
How to check op amp using multimeter
why some harmonics are disturbing while the others not
What is the difference between Droop vs Isoch Control?
What is the working of Field winding in dc motor, in which part is it work or why ?
In a house wiring why we are using only one neutral wire and so many phase wires from the main board, when the load is common for both wires?
ell me capacitor bank chossen formula.load in KW
We have a 1275KVA existing Transformer in a power plant project. Customer want to get it test & confirm whether it is a Dyn1 Transformer or not. Pleae let me know how to test it.
Why Batteries are rated as AH i.e AmpereHour,and its formula to converting AmpHour to Amp
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)