what is the diffrence between mcb &elcb?
Answer Posted / pillay
MCB is magnetic or thermal protected over current protection
device. that means if the current flowing through this mcb
exceeds the rating of the mcb it would trip. how fast it
trips depends on how much more than the rated current is
flowing through
ELCB is a device to detect any earth leakage current only.
If the leakage current exceeds the rated current the elcb
would trip off the circuit . The ELCB does not give
protection against overcurrent.
| Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
What is the power factor of an alternator at no load?
why the difference arise between HT reading & LT reading (submeters fixed in complexes, apartments etc)if the power factos exceed from 0.9 to 1 can the ht meter reads fast?
What is the different types of cable & current capacity of cable
What is ferro-resonance in electrical system? Why it occurs and what are measures to prevent it?
diff b/w normal grounding and resistance grounding
Explain the working of variable frequency transformer?
what is sevice settings for mccb?How can be it setted?
battery capacity use of made?
What are the advantages of nichols chart?
how we can calculate 2 phase welding transformer rating or total power?
What is the disadventage of gland earthing(power cable) if any. ?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
what work will do diffrential realay DG set
How PSV sizing being done