Three set (each phase contain 2 cable of 400 mmsq CU XLPE
AWA) of single core cables are connected to 11 KV motor of
14 MW & the switch gear supplay is taken from 11kv feeder &
this supplay taken from 275 KV substation. Problem is one
pair cable(L3- 2 cable ) getting very hot & gland melted
and damaged in switch gear side. the other two cable
haven't any more hot(ambient temp only & L3 haveing 95- 100
Degree C. The same problem happened in 275 KV substation
switch gear side also where the supply taken for 11 kv
switch gear. But here L2 phese cable had problem. Why it is
happening like this?. The cable having temperature
different at different location from gland side inthe case
of 11KV feeder of 275 kv substation. why ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
This happens whenever there is a loose connection or under -
sized lugs are used.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaviraj
Get a thermal imager or camera, you will see the loose
connection very easily. I also bet it's a loose connection.
Else one of the cable cores has been broken. Check for sharp
bendings on cable. Copper braids still connected/earthed
properly?
Is This Answer Correct ? | 0 Yes | 0 No |
How time response of the system is divided?
what happen when ac motor is connected with dc current
who invented electricity?
What is plc and how to do preventive maintenance
what happen if we give 220 volts dc supply to d bulb r tube light?
what is isochronous mod? what is voltage drop mode and p.f mode?
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.
what factor is necessary during design of HT & LT MOTORS.
what is deffrence between squirral cage and wound rotor in IM?
Why indicate only 440V to 3-phase supply.
why does a dc machine has high efficiency while working as a generator than as a motor