Three set (each phase contain 2 cable of 400 mmsq CU XLPE
AWA) of single core cables are connected to 11 KV motor of
14 MW & the switch gear supplay is taken from 11kv feeder &
this supplay taken from 275 KV substation. Problem is one
pair cable(L3- 2 cable ) getting very hot & gland melted
and damaged in switch gear side. the other two cable
haven't any more hot(ambient temp only & L3 haveing 95- 100
Degree C. The same problem happened in 275 KV substation
switch gear side also where the supply taken for 11 kv
switch gear. But here L2 phese cable had problem. Why it is
happening like this?. The cable having temperature
different at different location from gland side inthe case
of 11KV feeder of 275 kv substation. why ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
This happens whenever there is a loose connection or under -
sized lugs are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaviraj
Get a thermal imager or camera, you will see the loose
connection very easily. I also bet it's a loose connection.
Else one of the cable cores has been broken. Check for sharp
bendings on cable. Copper braids still connected/earthed
properly?
| Is This Answer Correct ? | 0 Yes | 0 No |
what you mean by frequency of an igbt& how to find it?
why current is leading in capacitor?
when we catch any one of the phases with our both hands in air(without touching ground),our body acts as a conductor.is it correct.please clarrify it.
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
where transformer is installed? a)generating station b)substation c)voltage regulating area
which pole motor is best ?4 pole motor or 6 pole motor,why?
is there any role of power factor with frequency variation? and how we can manage the frequency variation?
what is tan delta point in a current transformer?
Why star delta starter is preferred with induction motor?
Why HT cable have only 3 core ?
what power factor should we maintain to get maximum benefits our organisation load is 10 MW? is it best to maintain the PF at .96 rather than Unity to save electricity bill?
What is the power ratio between power in Star and Delta circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)