When generator breaker opened at full load. Subsequently the
generator prime mover will go to over speed.We can use place
the breaker between generator and transformer through bus
bar. Because transformer was transmitting the power only.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / e.subhash
Not necessary, because generator is synchronising hence we need bus only.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pallab phukon
when a generator is disconnected from supply when it is
running at full speed,there will be mechanical vibration in
the rotor and may even break.so,if a generator should be
disconnected,we have to at first reduce the load.
| Is This Answer Correct ? | 1 Yes | 4 No |
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?
Resistance of a conductor in a close electrical ckt is practically zero why?
How colour picturetube works & how many year it will works.
what is effect of reverse c.t connection on metering.
In order that work may be done:(a) Two wires are necessary(b) The circuit must have a switch(c) Coal must be burnt(d) A supply of energy is required
how to calculate optimum loading for transformer?
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
How to increase solar cell efficiency ?
how you taken aotitude test
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
how to calculate the cable size for LT and HT power cables with detail explanation?
2 Answers Asset Developments, Bhel,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)