Answer / sathish n p
Take an example let tr rating is 2500KVA, 11KV/415v
TO calculate maximum loading on primary side
2500 X 10^3=1.732 X 11 X 10^3 X I
I=131.01Amps
Similarly Secondary side
2500 X 10^3=1.732 X 415 X I
I=3478 Amps
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / debashis
For determining the optimum loading of a transformer we need
to determine the load for which my copper loss would be equal to my iron loss.
At this point the loss would be at its minimum level and hence
the efficiency would be maximum.
Remember Iron loss is independent of load and copper loss depends on the load.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / elminshawy
Sorry Vikadeny
But how it is optimum if I bought a 100MVA transformer and
I only loaded it to 50MVA or 70MVA ?
for optimum loading of transformers please refer to IEC
standard (60354 Loading guide for oil-immersed power
transformers )
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajendran
I think question refers to the optimum loading at which the
efficiency of the transformer is more/maximum...
if it is like that then we can refer the loading curves
provided by the manufacturer of the transformer....
generally as a thumbrule the optimum loading point is
around 85 to 95 percent of the capacity..
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vikadent
As a rule of thumb, the optimum loading is between 50% to 70
% and my reference is Electrical installation guide by
Schneider and this is the range where the losses are minimum
inside the transformer.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / khalid hussain shaikh
POWER=1.732*VOLTAGE*CURRENT*POWER FACTOR
HERE POWER=2500KVA
VOLTAGE=11 KV
POWER FACOR AS STANDARD=0.85
I=?
I=2500KVA/1.732*11KV*0.85
KV CANCELLED EACH DENOMINATOR AND NUMARATOR,
I=2500/1.732*11*0.85
I=154 AMP (11 KV SIDE)
I=2500 KVA/1.732*415 V*0.85
V CANCELLED EACH DENOMINATOR AND NUMARATOR
I=2500 K/610.963
I=4.091 KA
I=4091 AMP
| Is This Answer Correct ? | 10 Yes | 16 No |
What is fault level?How it is calculated and how it is Expressed?
what are the main hormonics in ac?
STATE AND EXPLAIN SUPER POSITION THEOREM.
What is mean 2XWY
How feedback transformer works to feedback power in Slip Power Recovery System
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
What is mathematical model of a control system?
What is PMG and AREP excitation system in generator
how to find insulation resistance of a generator(11kv) by theoritical formula??
what are fluorescent lamps (fluorescent fixtures) & what are incandescen lamps (incandescents fixtures) ? differences between these two ?
There are 2 motors without name plate and terminal but one is DC motor and another is induction motor.How one can identify which one is DC and which one is AC motor?
Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)