how to calculate optimum loading for transformer?
Answers were Sorted based on User's Feedback
Answer / sathish n p
Take an example let tr rating is 2500KVA, 11KV/415v
TO calculate maximum loading on primary side
2500 X 10^3=1.732 X 11 X 10^3 X I
I=131.01Amps
Similarly Secondary side
2500 X 10^3=1.732 X 415 X I
I=3478 Amps
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / debashis
For determining the optimum loading of a transformer we need
to determine the load for which my copper loss would be equal to my iron loss.
At this point the loss would be at its minimum level and hence
the efficiency would be maximum.
Remember Iron loss is independent of load and copper loss depends on the load.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / elminshawy
Sorry Vikadeny
But how it is optimum if I bought a 100MVA transformer and
I only loaded it to 50MVA or 70MVA ?
for optimum loading of transformers please refer to IEC
standard (60354 Loading guide for oil-immersed power
transformers )
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajendran
I think question refers to the optimum loading at which the
efficiency of the transformer is more/maximum...
if it is like that then we can refer the loading curves
provided by the manufacturer of the transformer....
generally as a thumbrule the optimum loading point is
around 85 to 95 percent of the capacity..
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vikadent
As a rule of thumb, the optimum loading is between 50% to 70
% and my reference is Electrical installation guide by
Schneider and this is the range where the losses are minimum
inside the transformer.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / khalid hussain shaikh
POWER=1.732*VOLTAGE*CURRENT*POWER FACTOR
HERE POWER=2500KVA
VOLTAGE=11 KV
POWER FACOR AS STANDARD=0.85
I=?
I=2500KVA/1.732*11KV*0.85
KV CANCELLED EACH DENOMINATOR AND NUMARATOR,
I=2500/1.732*11*0.85
I=154 AMP (11 KV SIDE)
I=2500 KVA/1.732*415 V*0.85
V CANCELLED EACH DENOMINATOR AND NUMARATOR
I=2500 K/610.963
I=4.091 KA
I=4091 AMP
| Is This Answer Correct ? | 10 Yes | 16 No |
in transmission line, if the load is suddenly increased at the receiving end of the system the phase shift will (a)decrease (b)becomems zero (c)increase (d)not be affected
what is distribution board?
explain PV modules in solar energy generation.
what happens when back charging of transformer is done for longer period
what is the diference beteween dedicated earthing & body earthing?
If the maximum demand is 120 KVA in a building, then what is the Current taken according to load given ? Formula for it ?
What is PIR (pre inserting resistance) in 400kv EHV SF6 BREAKER? Why it use?
132 KV TRFO BUSHING BURNT WHEN A 6.6KV HAS BEEN APPLIED TO IT .WHY .ANY REASON ?
Type of cable insulation?
11kv has three live wires how much voltage is in its single wire(leaving the other two wires)
Tell me the reason of connecting domestic t/f primary in star or delta,and also secondary side.
explain safety measures in alternator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)