Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate optimum loading for transformer?

Answers were Sorted based on User's Feedback



how to calculate optimum loading for transformer?..

Answer / sathish n p

Take an example let tr rating is 2500KVA, 11KV/415v

TO calculate maximum loading on primary side
2500 X 10^3=1.732 X 11 X 10^3 X I

I=131.01Amps
Similarly Secondary side
2500 X 10^3=1.732 X 415 X I

I=3478 Amps

Is This Answer Correct ?    33 Yes 5 No

how to calculate optimum loading for transformer?..

Answer / debashis

For determining the optimum loading of a transformer we need
to determine the load for which my copper loss would be equal to my iron loss.

At this point the loss would be at its minimum level and hence
the efficiency would be maximum.

Remember Iron loss is independent of load and copper loss depends on the load.

Is This Answer Correct ?    8 Yes 2 No

how to calculate optimum loading for transformer?..

Answer / elminshawy

Sorry Vikadeny
But how it is optimum if I bought a 100MVA transformer and
I only loaded it to 50MVA or 70MVA ?

for optimum loading of transformers please refer to IEC
standard (60354 Loading guide for oil-immersed power
transformers )

Is This Answer Correct ?    2 Yes 0 No

how to calculate optimum loading for transformer?..

Answer / rajendran

I think question refers to the optimum loading at which the
efficiency of the transformer is more/maximum...


if it is like that then we can refer the loading curves
provided by the manufacturer of the transformer....

generally as a thumbrule the optimum loading point is
around 85 to 95 percent of the capacity..

Is This Answer Correct ?    6 Yes 5 No

how to calculate optimum loading for transformer?..

Answer / vikadent

As a rule of thumb, the optimum loading is between 50% to 70
% and my reference is Electrical installation guide by
Schneider and this is the range where the losses are minimum
inside the transformer.

Is This Answer Correct ?    0 Yes 3 No

how to calculate optimum loading for transformer?..

Answer / khalid hussain shaikh

POWER=1.732*VOLTAGE*CURRENT*POWER FACTOR
HERE POWER=2500KVA
VOLTAGE=11 KV
POWER FACOR AS STANDARD=0.85
I=?
I=2500KVA/1.732*11KV*0.85
KV CANCELLED EACH DENOMINATOR AND NUMARATOR,
I=2500/1.732*11*0.85
I=154 AMP (11 KV SIDE)
I=2500 KVA/1.732*415 V*0.85
V CANCELLED EACH DENOMINATOR AND NUMARATOR
I=2500 K/610.963
I=4.091 KA
I=4091 AMP

Is This Answer Correct ?    10 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

What is fault level?How it is calculated and how it is Expressed?

2 Answers  


what are the main hormonics in ac?

1 Answers  


STATE AND EXPLAIN SUPER POSITION THEOREM.

3 Answers   ABB,


What is mean 2XWY

0 Answers   Wilo,


How feedback transformer works to feedback power in Slip Power Recovery System

2 Answers  


What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation

0 Answers  


What is mathematical model of a control system?

0 Answers  


What is PMG and AREP excitation system in generator

3 Answers  


how to find insulation resistance of a generator(11kv) by theoritical formula??

1 Answers  


what are fluorescent lamps (fluorescent fixtures) & what are incandescen lamps (incandescents fixtures) ? differences between these two ?

1 Answers  


There are 2 motors without name plate and terminal but one is DC motor and another is induction motor.How one can identify which one is DC and which one is AC motor?

6 Answers  


Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.

0 Answers   SK Engineering,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)