How to calculate PF capactors for a connected load?
Answers were Sorted based on User's Feedback
Answer / ramji
First calculate the actual KVAR load.Then calculated the
actual PF.Then as per required PF, calculate the KVAR to be
added.This is the value of capacitor bank to be shunted.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g parsaram reddy
capacitor bank selection base on the connected load
ex - 500kw load formula is kvar = kw ( tan cos-1pf) - (tan cos-1pf)there is power factor taken lower and higher valu , ex2 kvar= 250(tan cos-1 0.8)- (tan cos-1 0.96)step2 kvar=250(tan36.36-tan16.26) than 250(0.74-0.29) than250(0.45)than kvar=114.5this is required
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the insulation standerds for eg H clase and how many insulation standerds are there and its standerds??????
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
why open-delta core of 11kv Potential Transformer is 11000v/1.732/110/3?
how do we know the LT or HT panel trip by some broblem which indication willshow
what will happen when square wave is fed into input side of 3kva transformer and what you will get on output side.
what is the effect of power factor of machines in starting current
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
Car battery + terminal allways biger than - terminal! Why?
why on axial hitting up of air blast on hydrogen produced in oil circuit breaker,temperature rises of the core of the arc?
what is the formula for calculating motor rating? Example: If we want to rotate a 1000 kg waight disc up to 100 RPM, which size motor will require?
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)