from which formula we select a capacitor rating?
Answers were Sorted based on User's Feedback
Answer / karthik_elec
in single phase:
((V*I)/1000) KVAR OR 2*PIE*f*C*V2 * 10 power of -9
C means Capacitance in micro farad abd V squre2 is line
voltage
in three phase:
((root3*V*I)/1000) KVAR OR 4*PIE*f*C*V2 * 10 power of -9
C means Capacitance in micro farad between the line
terminals and V squre2 is the voltage between the phases
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / dhinakaran.s
capacitance is the ability of a body to hold an electrical
charge. Capacitance is also a measure of the amount of
electrical energy stored (or separated) for a given
electric potential.
Capacitance is given by C = Q/V farad.
The SI unit of capacitance is the farad; 1 farad is 1
coulomb per volt.
In parallel plate capacitor,
C=εA/d farad.
where
ε=ε0*εr
C is the capacitance;
A is the area of overlap of the two plates;
εr is the relative static permittivity (sometimes called
the dielectric constant) of the material between the plates
(for a vacuum, εr = 1);
ε0 is the electric constant (ε0 ≈ 8.854×10−12 F m–1); and
d is the separation between the plates.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / vikas kumar
xc=2Ï€fc
where: xc=capacitance
f= frequency
c= capacitor
Is This Answer Correct ? | 1 Yes | 1 No |
what is power factor? how can we correction the power factor if this is high or low? If anyone know please please send the answer on my email id ( kumarkirshan@in.com )
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?
What is minimum phase system?
WHY POLARITY TEST OF CT IS VERY IMPORTANT IN SWITCHGEAR
what is the full load current and power rating of 1 Tonne Air Conditioner?How will Calculate?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What will happen if we parallel two transformer with different %impedace?
single phase brower fan with control starter. *problem is when operate it.It will be trip.
how to calculate the watts from the tr
How can we check ELCB trip current sensitivity How can we check earth resistance value
An electric bulb giving light but at the time of lighting which one it takes? voltage or current
full form of electrical?