What is power factor ?What are the benefits of improved
power factor & how. Please explain with examples.?
Answers were Sorted based on User's Feedback
Answer / mehul g. c.
power facter - it is the sine angle between voltage vecter
and current vecter.
suppose you have 1.5 kw watt motor running on 230 volts and
power facter of your motor is .65 than your current requirement
i =p/volts*power facter
i =1500/230*0.8
i =8.15 amp.
and if you will improve power facter of your motor up to
0.85 than current requirement is
i=p/volts*power facter
i=1500/230*0.85
i=7.67 amp.
as you can see current taken by your motor is less if you
will improve your power facter.
advantages in big inductive machine & load.
1) current is less so losses should be less.
2) less current decrease your cable size & cost
3) voltage regulation should be good.
4) rating of switch gear will less.
and finally you will get some advantages from government if
you have big factory.
Is This Answer Correct ? | 30 Yes | 6 No |
Answer / dhivyabharathi
Hai Mehul, Power factor is the cosine of angle between
voltage and current. u have given sine of angle...
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ramesh
Generally power Factor are defined as the ratio between
Realpower(KW)/KVA (apprent power)
For ex- 8/10=.8
For kw= kva *.8
63*0.8=50.40kw
If power factor increses to .9 then
63*0.9=56.70
so the value kw increses if power factor increses
which indicates low current conjunction
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul g. c.
hai ramya.
there is a lot of way to increase power facter of your
machine or factory.
just read the book of b. l. thareja.
Is This Answer Correct ? | 4 Yes | 5 No |
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
In a 3 phase induction motor(without connecting supply) if we rotate its rotor by hand and check resistance of stator winding at motor terminal box its resistance varies why ??
what is main purpose of ignator in halogen lamps.how to identify the failer of ignator in circuit
i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.
how can i improve the power factor in domestic (230v)
How does HT work & Voltage required?
I have done my m.tech in electrical engg discipline. Can any one please suggest me how should I prepare for getting into phd in iit or nit.How should I prepare for getting into lecturership
why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently
what happens if generator is running leading power facotor?
why the neutral point is zero in star connection?
how the synchronizing is obtained at bus couplers in grid substation? (because there we cannot change the frequency in one of transmission lines like in generator synchronization)
Where can i get practical knowledge of solar system?