why the emf of a cell more than the terminal voltage when the
cell is delivering current?
Answers were Sorted based on User's Feedback
Answer / satish
The EMF is the elcromotive force independent of current
flow but when the current stats flowing in the circuit then
there i some voltage drop due to the internal
resistense.So,The net potential difference will be V=E-IR
where V is the voltage,
E is Electromotive Force,
R is internal resistance.
| Is This Answer Correct ? | 73 Yes | 16 No |
Answer / johnston
The EMF is the elcromotive force independent of current
flow but when the current stats flowing in the circuit then
there i some voltage drop due to the internal
resistense.So,The net potential difference will be V=E-IR
where V is the voltage,
E is Electromotive Force,
R is internal resistance.
| Is This Answer Correct ? | 18 Yes | 12 No |
Answer / abhishek-gaur
V=E-ir
there is som potential drop in internal resistnc of clll...
so terminal voltg is bit less
| Is This Answer Correct ? | 5 Yes | 10 No |
Answer / rakesh
it's necessary for curreny flowing in tha circuit .
beacause current flow high to low pd
, so that's required
| Is This Answer Correct ? | 8 Yes | 20 No |
is it possible to step down voltage of single phase from a three phase sysem? explain
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
what is the working principle of smoke detector in fire alarm system
what is the thumb rule to know current carrying capacity of copper conductors of different size.
How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts
i have 3, 75hp motors and 10, 15 hp motors....and to run this motors continously with a generator how much rating(kva) of generator will suiteble....?
5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch
what is cogging in motors?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
How much pole motor can be desion for 415 volt ,50 hz.Power supply. in pratical condition . Prakash veer singh
why abcd parameters are called as transmission parameter?
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)