Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why the emf of a cell more than the terminal voltage when the
cell is delivering current?

Answers were Sorted based on User's Feedback



why the emf of a cell more than the terminal voltage when the cell is delivering current?..

Answer / satish

The EMF is the elcromotive force independent of current
flow but when the current stats flowing in the circuit then
there i some voltage drop due to the internal
resistense.So,The net potential difference will be V=E-IR
where V is the voltage,
E is Electromotive Force,
R is internal resistance.

Is This Answer Correct ?    73 Yes 16 No

why the emf of a cell more than the terminal voltage when the cell is delivering current?..

Answer / johnston

The EMF is the elcromotive force independent of current
flow but when the current stats flowing in the circuit then
there i some voltage drop due to the internal
resistense.So,The net potential difference will be V=E-IR
where V is the voltage,
E is Electromotive Force,
R is internal resistance.

Is This Answer Correct ?    18 Yes 12 No

why the emf of a cell more than the terminal voltage when the cell is delivering current?..

Answer / abhishek-gaur

V=E-ir
there is som potential drop in internal resistnc of clll...
so terminal voltg is bit less

Is This Answer Correct ?    5 Yes 10 No

why the emf of a cell more than the terminal voltage when the cell is delivering current?..

Answer / rakesh

it's necessary for curreny flowing in tha circuit .
beacause current flow high to low pd
, so that's required

Is This Answer Correct ?    8 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

is it possible to step down voltage of single phase from a three phase sysem? explain

2 Answers  


What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?

0 Answers   JSW,


what is the working principle of smoke detector in fire alarm system

2 Answers   Vijaya Bank,


what is the thumb rule to know current carrying capacity of copper conductors of different size.

1 Answers  


How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts

1 Answers   Laurus,


i have 3, 75hp motors and 10, 15 hp motors....and to run this motors continously with a generator how much rating(kva) of generator will suiteble....?

2 Answers  


5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch

0 Answers  


what is cogging in motors?

1 Answers  


One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?

1 Answers  


How much pole motor can be desion for 415 volt ,50 hz.Power supply. in pratical condition . Prakash veer singh

5 Answers  


why abcd parameters are called as transmission parameter?

1 Answers   Accenture,


how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)