Answer / arun.giit
as all the losses is in the form of power;and in transformer
iron loss is directly propertional to voltage(V) &copper
loss is propertional to current(I).it is not depend upon
powerfactor,so it's rating is in KVA.
| Is This Answer Correct ? | 20 Yes | 1 No |
Cu loss of transformer depends upon current I and iron loos
depends upon voltage V...So as we can say that the total
losses of the transformer depend upon VA (volt-ampere) and
independent of phase angle between V & I (i.e. pf
angle)...so transformer rating is in kVA & nt in KW...
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / tin`
Becuase kVA is the 'total' apparent power. The load
connected to the transformer can have different power factor
(pf) and so the kW rating will vary according; kW=kVA*pf.
The transformer rating is stated in kVA in order to show
the full capacity of the transformer and then the real
power (kW) rating can vary with power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / salim
bcz
kw=kva×pf and load on tranz.is not constant.So pf is varies with load.thats why traz.rating is always in kva not in kw
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohan singh
Transformer ratings are in KVA because the power factor is
for the load on which transformer will operate is not known
in manufacturing and KW = V x I x Cos Phi.so it is Rated in
KVA and not in KW.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / peter
coz KW or HP makes no sense.....transformer is not a power
conerter involving mechanical energy.....i mean...it just
transfers electrical energy ....
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / bob
Because transformer is power source and active power and
reactive power drawn from it depend on load nutural.
| Is This Answer Correct ? | 1 Yes | 5 No |
what are the causes for strip heater failure ?
Is possible to increase the voltage without using transformer? why?
what is a starter ??
is there any current flows in our body?
Wghat is D-curve MCBs
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem
what is the use of permanent magnet generator in exciter
what is timing for mccb 800A tripping?
what is the star delta connetion and how can do it a three phase motor with control witing with picture
0 Answers Aurobindo, SA Kent, Wipro,
what do you mean by switchgears?
5 Answers Practical Viva Questions,
what is the working and construction of generator
Are we do it in single transformer with dual primary as 11 KV and 33 KV and constant output as 415 Volts?.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)