What should be the 28 days cube strength for M-25 grade
concrete?How it is connected with acceptance criteria of
fck+3 as per IS 456-2000 and why?
Answers were Sorted based on User's Feedback
Answer / viki
the 28 days cube strength for M-25 grade
concrete should be 25N/mm2.
acceptance criteria are some conditions defined by IS 456
regarding characteristic strength of concrete when the mix
is prepared on site.strength tests are performed on 4
blocks of concrete.avg strength is calculated.
then fck+3 means that the avg strength of the concrete mix
at the site should be 3N/mm2 greater than fck of mix.
i.e. mean strength= (fck+3)N/mm2
(refer IS456 CLAUSE 16)
| Is This Answer Correct ? | 18 Yes | 7 No |
Answer / p c debnath
fck +3 is the average/mean strength of four consecutive set
of cube
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ashwani kumar
AFTER 28 DAY M-25 GRADE CUBE STRENGTH IS 25 N/MM2 , ITS
ACCEPTANCE CRITERIA IN THE IS-456, FCK+3 IS AVG
CHARACTERSRICK SRENGTH OF CONCRETE.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / n pandian
The quality of concrete is acceptable only if both 1) and 2) are satisfied:
1) As per column 2 in Table 11 of IS 456 – 2000, mean of the group of 4
non-overlapping consecutive test results shall be greater than or equal to
a) (fck + 0.825s) N/mm2
where fck is the characteristic compressive strength of concrete;
s is the established standard deviation which is to be arrived for
atleast 30 samples as early as possible at site.
Note: In the absence of established standard deviation value assumed standard deviation values given in Table 8 of IS: 456-2000 may be used.
b) (fck + 3) N/mm2 for M15 or (fck + 4)for N20 and above
a) or b) whichever is greater
2) As per column 3 in Table 11 of IS: 456 – 2000, Individual test Results (ITR) shall be greater than or equal to (fck - 3) N/mm2.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the concrete mix design ratio of railway sleeper??????
What is Reason of Alkali-Silica reaction in Concrete mix and its remedies?
please what is the number of bars required for a column of 6mx6m and 450mmx300mm,its a commercial building (Church)
what do you mean by fe500d what is 500 n what's ,d,
how much cement consumption in box type waterproofing
In which code the the maximum height of concrete casting has been explained
WHAT IS THE DIFFERENCE BETWEEN FACTOR OF SAFETY AND PARTIAL SAFETY FACTOR?
how to check aggregate quantity in stock yard
how many shuttering material required for 1000 sq.m built up area.
Ihave 230mm *115mm * 75mm brick calculation in cft and 115mm brick calculation in sft
What is construction mitigation management?
What are the applications of the modulus of elasticity?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)