What is the difference in Line PT & Bus PT.
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
Line PT is connected in the incomer (line) to detect the
voltage of the incomer whereas bus PT is connected in the
bus, 1 before the bus coupler and another after bus
coupler, to detect voltage in the bus.
The main purpose of both of them is to sense the voltage so
that the breaker can get enough information to operate..
| Is This Answer Correct ? | 54 Yes | 1 No |
Answer / maloy
line pt is connected in incomer where the bus pt is connectd in the main bus bar though both funtioning the same for measurement & protection
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / muhammad abid ali shah
Line PT is used to measured the voltage and also used for voltage protection means that under voltage or over voltage and the bus PT is used for metering and measure the voltage of bus bar voltage.
| Is This Answer Correct ? | 4 Yes | 7 No |
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
Parts of machine and their discription in details with suitable photo
Zone of protection and tripping scheme of arc protection relay.
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
what is the acceptable value of TAN DELTA and dissipation factor for 11kV, 1.75HP Motor?.
What happent when a AC motor(no break and starters ) stop and suddenly start . ? Starting current low or high?? Why?
why we don't use air circuit breaker on H T line in place of vacuum circuit breaker ?
What is the Diff. btw Fire Alarm System & VESDA System??????
ouestion for the post of section engineer
why generator and t/f ratings given in kva & motor rating is in KW?
Is there is any difference between AC and DC Cables
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)