Answer / matt
Given a system power factor of 0.9, PFC unit of 50kvar we can work out the following
50/0.9 = 56 A real current
56^2 * 50^2 = 75 A apparent current
Cable capacity - 75 * 1.35 = 100 A
Factor of 1.35 used for over rated capacitors as per
industry standards.
Breaker shall be rated at less than the cable capacity but greater than 75A. Increase cable size to suit breaker breaker sizing if required.
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / mohan
Amps Per KVAR is between 1.1 to 1.3 Amps
for a 300KVAR panel
the current shall be 130 AMPs(and if the capacitors are
auto swithced , then switching surges need to be considered
hence) * 1.5 Times = 585Amps
The nearest breaker size is 630AMPS
It is preferable to use Capcitor duty contactor for
switching
| Is This Answer Correct ? | 1 Yes | 6 No |
how dose servo motor works
what is linear elements
can we increase our frequency rate in INDIA?
what is the principle of generator, motor, and transformer and explain the definiton of flemings left hand rule , right hand rule and ohms law
Anybody tell me about modbus hex address of l&t trivector meter er300p??I want to read voltage,current,kwh etc via rs485...If anybody have a manual then send on my mail..Brijeshmodi18@gmail.Com
when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?
Can we convert off load tap changer transformer to on load tap changer transformer
why and where we use early make & late break contacts in protection?
what is the differance between HT motors And LT MOTORS.
0 Answers Empire Vitrum Glass, Sappi,
Which of the following statements is incorrect?(a) 1N = 1 kgm/s2(b) 1V = 1 J/C(c) 30mA = 0.03A(d) 1 J = 1N/m
75 kw motor take 45 amp in no load delta in star 10 amp but in load it will take 160 amp but IR velue of winding above 500 at 1kw ph to earth and ph to ph. what problem it should be?
why dc series motor has high starting torque
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)