formula for incomer breaker size calculation of powerfactor correction unit..

Answer / nur.asidik

you need to consider of breaking capacity too

Is This Answer Correct ?    2 Yes 0 No

formula for incomer breaker size calculation of powerfactor correction unit..

Answer / matt

Given a system power factor of 0.9, PFC unit of 50kvar we can work out the following

50/0.9 = 56 A real current

56^2 * 50^2 = 75 A apparent current

Cable capacity - 75 * 1.35 = 100 A

Factor of 1.35 used for over rated capacitors as per
industry standards.

Breaker shall be rated at less than the cable capacity but greater than 75A. Increase cable size to suit breaker breaker sizing if required.

Is This Answer Correct ?    6 Yes 6 No

formula for incomer breaker size calculation of powerfactor correction unit..

Answer / mohan

Amps Per KVAR is between 1.1 to 1.3 Amps

for a 300KVAR panel

the current shall be 130 AMPs(and if the capacitors are
auto swithced , then switching surges need to be considered
hence) * 1.5 Times = 585Amps
The nearest breaker size is 630AMPS

It is preferable to use Capcitor duty contactor for
switching

Is This Answer Correct ?    1 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between CT and CVT in EHV Sub Stations

4 Answers   Hofincons, Lanco, TATA,


how to calaculate the amps in transformer ?

2 Answers  


is tree is a good conductor and it may be used for conductor?

3 Answers  


how to can we synchronize different capacity of DG sets.60kva& 250kva?

2 Answers   Power Plant,


I AM GOING TO ATTEND APTRANSCO ON 26TH OCT 08.PLEASE SEND ME ANY MATERIAL OR TYPE OF QUESTIONS OR EXP QUESTIONS.

0 Answers   Power Grid,






How to calculate the copper in HT motors if KW, RPM & Voltage is given

0 Answers   Control Dynamics, NTPC,


1)why the transformer rating in KVA insted of KW 2)why the secondary of ct is shorted and why the PT secondary is open

3 Answers  


Thermal withstand capability under full short circuit conditions, in terms of number of times of occurrence of short circuit and corresponding anticipated percentage reduction in transformer life.

0 Answers  


hi friend i am going too attend for hpcl in this month please help me by sending written test question papers i am in the stream of E.E.E

0 Answers   HPCL,


what is breathing?

0 Answers   PWD,


what is the working principle of DC generator ?

10 Answers   DRDL, HCL,


what is ic 01,ic 06 ?is it types of cooling?

0 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)