Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / er sushil saini

this is because whenever fault occur the ac supply will
also fail so protection system will not work and damage to
equipments can occur. DC supply in battery bank will always
be available in case of ac failure and protection system
will work and trip the breakers.

Is This Answer Correct ?    44 Yes 4 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / rd dadhich

1.It is very common practice to use battery with charger for
protection , operation & indication in HT switch gears due
to most relable system to work as after charging only
battery comes directly in line during failure of AC supply.
or power supply.

UPS can be used theoretically , but we are adding one more
week link in critical protection supply due to addition of
inverter. , as inverter is :-

AC supply . > Battery Charger > Battery > Inverter

Where as battery charger is only :-

AC supply . > Battery Charger > Battery

2. AC coils of tripping & closing are un common & bigger in
size.

Is This Answer Correct ?    11 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / kesavan.03

In the case of AC supply we can't reliable. However UPS is
available in any failure of UPS supply also will dangerous
for control system. As in the case of DC supply the battery
is charged & it is available whenever we need. So DC coils
are used for control purpose(Closing & Tripping),

Is This Answer Correct ?    8 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / er. manoj

Now consider a situation when there is a fault and coil supply is given AC, as we know in case of fault there is a voltage dip, so across the coil sufficient voltage would not build up to energize it. So DC is given across tripping or closing coil

Is This Answer Correct ?    2 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / jpgupta

how to check capacitor

Is This Answer Correct ?    2 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / ganesh yeole

hey friends.....I agreed ur ans but I feel one more thing...if we use AC supply to HT system....see you know well sign wave when wave going upper side then down....when wave coming down side you have to see 0 volt but HT tripping or closing coils or contactor pick up time not sufficiently working on there. it not working properly so you found there electrical damages. that's cause DC supply using in HT system. cause DC is directly pick up to coils.........if you are satisfied to my answer you mailed me ganesh.yeole89@gmail.com.......mob no. 09579853838

Is This Answer Correct ?    5 Yes 4 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / ankit

dc supply is used because response time in dc supply is fast as it does not have positive negative sinusoidal wave like ac supply
and in ht we need very fast switching in microseconds

Is This Answer Correct ?    1 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / jp gupta

why can check Ignitor thas its ok or not

Is This Answer Correct ?    0 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / satyanarayana

Suppose if breaker was tripped on under voltage then Ac supply is not available at that instant so that breaker will not trip if AC supply is used for breaker closing and tripping.

Is This Answer Correct ?    1 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / avd

Fundamentaly UPS AC supply can be used. But you are
investing more in UPS than the battery charger. Remember
UPS will have inverter section also.

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?

0 Answers   TMB,


when we put inducter in neuteral grounding of genrator.

3 Answers  


explain safety measures in alternator?

0 Answers  


Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1.  H1-H2 = H2-H3 H3-H1 2.  H2-H3 = H3-H1 H1-H2 3.  H3-H1 = H1-H2 H2-H3 For the LV side also: 4.  X1-X0 = X2-X0 X3-X0 5.  X2-X0 = X3-X0 X1-X0 6.  X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0  H2-H0  H3-H0    X0-X1  X0-X2  X0-X3 128.0  119.9  7.2      29.2   13.3   15.8 70.7   128.4  59.2     23.4   22.0   3.6 7.2    120.1  128.1    13.4   29.3   15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?

0 Answers  


11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter

0 Answers  






please send me the L&T Emb. sys. placement papers and entire details of pattren

0 Answers   HMM, L&T,


why are distributed windings generally used in alternators?

0 Answers  


How many different speeds can be obtained in cascade control of two induction motors?

1 Answers  


how to calculate the multiplying factor for energy meter with CT ratio given

23 Answers   Bhel, Dalmia Group, DIFC, Fedco, Hindustan Unilever Limited, Lupin, MahaDiscom, MAL Pakistan, Myunghwa Automotive, Panchshil Infrastructure, Regala, RVPN, VIPL,


what is the use of expulsition protective gap in 11Kv line.

0 Answers  


What is NGR . What is the purpose of 10 sec ,60 sec rating of NGR.

0 Answers   KOTC,


How will earthing is making for Aeroplane?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)