Why dc supply is used for closing and tripping coil of ht
breakers. What happen if we use only ups ac supply only.
Answers were Sorted based on User's Feedback
Answer / er sushil saini
this is because whenever fault occur the ac supply will
also fail so protection system will not work and damage to
equipments can occur. DC supply in battery bank will always
be available in case of ac failure and protection system
will work and trip the breakers.
| Is This Answer Correct ? | 44 Yes | 4 No |
Answer / rd dadhich
1.It is very common practice to use battery with charger for
protection , operation & indication in HT switch gears due
to most relable system to work as after charging only
battery comes directly in line during failure of AC supply.
or power supply.
UPS can be used theoretically , but we are adding one more
week link in critical protection supply due to addition of
inverter. , as inverter is :-
AC supply . > Battery Charger > Battery > Inverter
Where as battery charger is only :-
AC supply . > Battery Charger > Battery
2. AC coils of tripping & closing are un common & bigger in
size.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / kesavan.03
In the case of AC supply we can't reliable. However UPS is
available in any failure of UPS supply also will dangerous
for control system. As in the case of DC supply the battery
is charged & it is available whenever we need. So DC coils
are used for control purpose(Closing & Tripping),
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / er. manoj
Now consider a situation when there is a fault and coil supply is given AC, as we know in case of fault there is a voltage dip, so across the coil sufficient voltage would not build up to energize it. So DC is given across tripping or closing coil
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ganesh yeole
hey friends.....I agreed ur ans but I feel one more thing...if we use AC supply to HT system....see you know well sign wave when wave going upper side then down....when wave coming down side you have to see 0 volt but HT tripping or closing coils or contactor pick up time not sufficiently working on there. it not working properly so you found there electrical damages. that's cause DC supply using in HT system. cause DC is directly pick up to coils.........if you are satisfied to my answer you mailed me ganesh.yeole89@gmail.com.......mob no. 09579853838
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ankit
dc supply is used because response time in dc supply is fast as it does not have positive negative sinusoidal wave like ac supply
and in ht we need very fast switching in microseconds
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / satyanarayana
Suppose if breaker was tripped on under voltage then Ac supply is not available at that instant so that breaker will not trip if AC supply is used for breaker closing and tripping.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / avd
Fundamentaly UPS AC supply can be used. But you are
investing more in UPS than the battery charger. Remember
UPS will have inverter section also.
| Is This Answer Correct ? | 2 Yes | 4 No |
Why use prefer Dc drive in place of Ac drive for kiln Operatio in Cement Plant?
what are the advantages and disadvantages of oil filled cables over XLPE cables
what happens when back feeding supply accidently collapses with normal supply ??? How?? [that is sometimes in a substation 11kv feeder if their ws long time permit work, back feeding supply will provide from nearest substation... if accidently after the permit work,they charged the feeder without removing back feeding wat will happen...?]
Is there any reason that a vertical motor can not be mounted horizontally ? I happen to have one and would like to use it horizontally to save money by not buying a new horizontal motor.
what are types of encoder
block diagram of 2 ups system connected in parallel mode?
how to measure the transformer resistance values(dyn11)?and howmuch the minimum value?
why DC motor body is plain cover but AC motor is different like finse?
Why we does earthing for transformer neutral point
what is automatic voltage regulator and it is used?
Anybody tell me about modbus hex address of l&t trivector meter er300p??I want to read voltage,current,kwh etc via rs485...If anybody have a manual then send on my mail..Brijeshmodi18@gmail.Com
Why increase in current leads to increase in conductor temperature?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)