IF we have 500kva transformer & know the current on HT & LT side, how can we consider for its breaker?
Answers were Sorted based on User's Feedback
breaker rating is selected near to the calculated current of equipment and standard rating of breakers. but it is very important to know the fault current of that
system/ckt where it to be attached.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kshirod
all are wrong
am telling you a simple method
always follow the thumb rule which is 500kva*1.39=695amp
bt every transformer can take extra 10% amp load
so you can use 800 amp mdo typae 3 pole l&t make acb in the
lt side
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maze one
S = I x V x sq. root of 3
where:
S = Apparent Power, VA
I = Current, A
V = Voltage, V
note : use sq. root of 3 if the system is 3 phase
let's say Voltage = 460V @ Secondary Side
I = (500,000 VA)/(460V)(sq. root of 3)
I = 1,882.66 A
you may multiply the safety factor by 125% to 250%
or using inversed time circuit breaker by 250%
I will use 125% only, that is safe
I = 1882.66 x 125%
I = 2,353.325 AT
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / roy
ROUT 3*V*I=KVA
SO FIRST YOU SHOULD MENTION THE VOLTAGE.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / jords
for single phase- 500,000 divided by the voltage times 80% for
your safety factor equals your C.B. size.
for three phase- 500,000 divided by the voltage divided by
square root of three times 80% for your
safety factor equals C.B. size.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is leading and laging please in details
Why is the generator rating always in kVA and motor rating in kW?
What is d diff. btw MCB & MCCB???
Please specify the parts of VCB&ACB
IN dc capacitive reactance is??
number of I/O devices in siemense plc
what about the input current fan when regulator regulates to speed low?
how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p & 100 h.p. then what rating of transformer we can select. urgent. pls reply
When Alarm report at LED,Alarm volatge is 11-13 Volt But LED is of 3 volt.then why not it burn?
Testing procedure of DG alternator stability test
Can we convert off line transformer to on line transformer
Why semi-conducting insulation is used in XLPE cables?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)