what is meant by trip circuit supervision & directional or
non directional over current ?
Trip circuit supervision is for supervision of trip circuit
for loss of DC supply,faults on trip coil or cables,faults
in auxiliary contacts and in itself, with breaker in any
position.Directional OCR acts for over current in one
direction only where non-directional acts for both the
directions
| Is This Answer Correct ? | 9 Yes | 1 No |
why voltage swells and dips in transmission line?
why transformer rating is expressed in kva.
What is the unit of vaccum?
what will happen if the connections of protection ct reverse? will it burn the ct?
Hi i want to know that in generation station what we are generate either voltage or current
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
An electric bulb giving light but at the time of lighting which one it takes? voltage or current
effect of single phase transformer on full load current?
whether a separate starter is used for a motor while it is connected to a vvvf panel?
What is the capacity of the Fastners 12mm?
Explain the different methods used in the choice of rotor slots for reduction of harmonic torques in an induction motor.
in telecom we are using neutral?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)