Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why we are not using capacitor in line when load on Genset?

Answers were Sorted based on User's Feedback



Why we are not using capacitor in line when load on Genset?..

Answer / virendra

because the reactive prower produce by the Capcacitor may
harm the AVR of the DG set

Is This Answer Correct ?    4 Yes 2 No

Why we are not using capacitor in line when load on Genset?..

Answer / kadiresan.k

whether the load is on EB or DG, p.f to be maintained close
to unity and the type of load to be studied and capacitor
to be connected accordingly. The Capacitors to be switched
ON and OFF according to the load with the help of APFC
panels / Controllers. In case of load shedding time, the
concerned capacitors to be tuned off immediately, else it
will result in over voltage at the system if the load is on
DG side. So the power system to be optimised to handle the
load in both EB and DG with proper power factor correction
systems.

Is This Answer Correct ?    2 Yes 1 No

Why we are not using capacitor in line when load on Genset?..

Answer / william lobo

By putting capacitor on Genset what we are doing is only
loading the genset additionally.
Capacitor is used to improve the power factor of the
system. This is important for the power supply cos; hence
they insist that pf should be 0.9 or thereabout.
Hence it is compulsory to use Capacitors to improve the PF
if below 0.8 or they will fine you.
When using a gen set we have to see what is the type of
load. If it is motor load inductive then we have to switch
on some of the capacitor banks only.

Is This Answer Correct ?    3 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

how ELCB drip when earth and phase touch together?

2 Answers  


Is there any difference between load based power plant and coal based power plant?

1 Answers  


what is the ideal earth resistance

11 Answers   Amit Enterprises, Enercon,


when any relay trips in any ckt then what type of setting is there in motor?what is function of relay in that ckt?

3 Answers   Finolex,


Operation of isolators.

0 Answers   KSEB, L&T, Siemens,


Why transformer, generator, ups rating kva?

2 Answers  


CAN ANYBODY PL TELL ME WAT FACTORS CAN CAUSE UNDERVOLTAGE ON A BUS??? PL LIST ALL THE REASONS WITH SOME EXPLAINATION

3 Answers  


How does a system control centre in a utility plant gets the grid frequency of the electrical network (50 Hz or 60 Hz)by the SCADA system?

1 Answers  


We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?

1 Answers   PDP Steel,


for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?

0 Answers   Power World,


What is the role of Dedicated earthing in UPS System?

0 Answers   HCL, MSPL,


difference bteween neutral grounding resistor and neutral grounding transformer??

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)