how we have to calculate the short circuit current for
33/11kv 2mva, 7.5% Z, Transformer primary side breaker and
secondary side breaker short circuit current for both sides?.
Answer Posted / dipak
Short Circuit Current=mva/z=2/.075=2.67MA,rating of
transformer is always same for primary or secondary
| Is This Answer Correct ? | 2 Yes | 6 No |
Post New Answer View All Answers
Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?
Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.
sir, i am 3 years diploma course pass out candidate.what type of certificate can i got in marine service.
what is meant by motor startup supervision & motor load jam protection ?
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
How DC earth leakage currents can be reduced ?
what kind of technical test that i need to learn because i have an interview tomorrow.. please someone help me..
what is transformor oil gread
Why do we perform an open-circuit test and short-circuit test on the transformer?
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
According to conduit size which size wiring & how many wires can we provide wires in conduit & how can we select conduit size accordingly?
what is mean by drives?
HI....HOW CAN BE MESARED THE VALVE OF NEUTRAL GROUND RESISTOR WHIC IS LOCATED AT SWICHGEAR ON GENERATOR SIDE....
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator