How to calculate HV Cable Sizing & what are the factors to be considered for selection?...

Answer / ashish tiwari

The HV cbale size shall be base on the fault level on HV
side. Like 18.4KA fault current for 11 KV supply & 21.34 KA
fault current for 33 KV supply. We can calculate the HV
cable
BY USING FORMULA ISH = K x A/( sq. root of T)


Where,
ISH :SHORT CIRCUIT CURRENT IN KA (r.m.s.)

T :DURATION OF SHORT CIRCUIT CURRENT IN SECONDS

A :AREA OF ALUMINIUM CONDUCTOR IN MM2

K :IS A CONSTANT = 0.094 for aluminium

ISH x Sq.rootT 18.4 x Sq. root 1
A = ------------ = ------------
K 0.094
= 195.7 sq.mm

HENCE 3 C x 240 SQ.MM XLPE (AL) CABLE IS REQUIRED FOR
INCOMING SIDE AS WELL AS OUTGOING SIDE OF 11 KV SUPPLY.

Is This Answer Correct ?    32 Yes 19 No

How to calculate HV Cable Sizing & what are the factors to be considered for selection?...

Answer / ali

i want calcuiate the size of hv 6.6kv cable can trans 750 amper

with regard

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is AVR in alternator how its work?

8 Answers  


what is over cureent protection

3 Answers   Anil Group, MPSEB,


which surface is suitable for NEUTRAL GROUNDING ?

1 Answers   NTPC,


Is it required to use Automatic transfer Switch in L&T panel board if we use AMF panel with DG set? How the single line diagram will be? Please forward the material to sreenu_207@yahoo.co.in

0 Answers   HAL,


why autotransformers are not safe for supplying low voltage from a high voltage source?

5 Answers  






in telecom we are using neutral?

1 Answers  


Is motor current is dependent on load.

2 Answers  


What will Happened if the polarity of CT is changed?

13 Answers  


2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?

5 Answers   Imdaad,


What loads the lagging and leading effects comes in a circuit?

5 Answers  


Technical specification of a wind farm

1 Answers  


why secondary terminal of current transformer should not be open circuited?

4 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)