How to calculate the Airconditioner capacity for a standard
telecom BTS shelter?
Answers were Sorted based on User's Feedback
Answer / gajanan bharad
I am too seeking right answer, but I know that the calculations above are incorrect. We have to consider the heat generated by BTSs and not the power consumed by BTSs. We have to take into account the heat generated/ rate of heat generation in Watts by all the equipment inside the shelter. There are 48V SMPS, Battery sets, BTSs, Microwave equipment, lights and assume 2 persons working. Heat generated by the SMPS equals input power minus the output power (i.e. loss of energy in terms of heat). But for rest items need the information on heat generated. Then only we can arrive at correct air conditioner capacity requirement.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suraj.dahiya
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
plus surface area of BTS shelter suppose (9feet*6 feet)=54
sqft area.
required temp =54*25=1.350 kw
so total kw = 18.4+1.350=19.7KW
total Tr. required to cool the shelter @25 C =19.7/3.5
=5.6 Tr. AC required
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / chandrashekar
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
Is This Answer Correct ? | 3 Yes | 9 No |
What is the problem of internal failure in ship engine telegraph system norcontrol?
hy i need help with LabView, I need a sample code of LabView to download serial data from the Intellivue Patient Monitor to PC. Thank you in advance.
what is the working principle of Brushed alternator ? without exictation how we can give dc supply to rotor ?
What is breather? why we use it ?
what is the function of breather in a transformer
29 Answers Areva, Bhel, RKM Powergen, Vijai Electricals,
how can we find a burden of potential transformer? what does it effects? how can we calculate rated load of it?
what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?
What is meant by Energy Efficient Transformers??? give significance
when we catch any one of the phases with our both hands in air(without touching ground),our body acts as a conductor.is it correct.please clarrify it.
What will happen if the d.c. Shunt motor opened accidentally running on no-load has its shunt field winding?
What is meant by harmonic distortion?
carbon zinc cell voltage?