Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?

Answers were Sorted based on User's Feedback



How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / gkg

For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw

passive load calc ok.

Is This Answer Correct ?    51 Yes 10 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / chandrashekar

Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.

Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency

i.e KVA=KW/PF


Example to calculate the rating of DG.

If total Load is available 15Kw both active and Passive
then

we should apply above formula KW=KVA*0.8

15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA








Active Load Calculation:

Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A

Total Active load is P=VI P=230*28=6.4KW

Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient

NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.

Is This Answer Correct ?    56 Yes 25 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / dhananjay vats

VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?

5 Answers  


in a refinery one motor is suddenly stoped. what will do how can i findout the problem explain step by step

2 Answers  


why Line voltage =1.732XPhase voltage what mean by 1.732

4 Answers   IBM, NCC,


What is the Different Between Breaker and One and half breaker.

2 Answers  


What is meant by class of CT&PT?

1 Answers  


what is green house effect?

4 Answers  


What are the different lines and what are the different types of losses occur on them?

2 Answers  


differentiate between c curve and d curve MCBS?

1 Answers  


i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.

0 Answers   Bay Fishing Corporation,


why grid failure happens?

1 Answers  


in my observation NCT is used at Karnataka power transmission. why we are not used in andhra pradesh

1 Answers  


in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)