How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
| Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
| Is This Answer Correct ? | 4 Yes | 1 No |
a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?
in a refinery one motor is suddenly stoped. what will do how can i findout the problem explain step by step
why Line voltage =1.732XPhase voltage what mean by 1.732
What is the Different Between Breaker and One and half breaker.
What is meant by class of CT&PT?
what is green house effect?
What are the different lines and what are the different types of losses occur on them?
differentiate between c curve and d curve MCBS?
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
0 Answers Bay Fishing Corporation,
why grid failure happens?
in my observation NCT is used at Karnataka power transmission. why we are not used in andhra pradesh
in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)