How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
| Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
| Is This Answer Correct ? | 4 Yes | 1 No |
What is ics,icu,icw of load breaker
hoW to select a CT?
circuit breaker work alone during fault condition or need any relays ?
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
what kvrah y we need to take the readind of that
If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.
Pl. give me checklist for installation & commissioning of machine tool.
why nutral and earthing wire connect with each other in main panel board.
how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.
What is the role of power pack in substation protection system?
Explain about p.t?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)