How to calculate cable size for a particular load? i have 12
MW,11KV Motor 3 Phase, what should be cablesize?
What are the points to remember for cable sizing calculations?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
For Cal.the cable size , pl. see the below size
1) Cal. the full loasd current of motor
2) cal. the voltage drop from ht starter panel to motor at
starting and running .
3) as per IEC rule u should take the 20% additional to ur
selected size of cable.
Base on the above step we can easily cal. the size of cable
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / manoj
Calculate steady state voltage drop and motor starting voltagedro they should be within limit also the short circuit withstand capacity to satisfy i2t
Is This Answer Correct ? | 0 Yes | 2 No |
why rating of alternator in kva & induction motor in kw
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?
what is the formula to calculate voltage drop/loss on 66KV Transmission Line?
Transformer Parallel Operations
what is power factor in ac ckt ?
What happen while we measure the Current in Rotor?
what is the term of desruptive voltage
5 Answers Bhel, Energy Infratech,
what is current check gurd relay?
Why does the DC voltage needed is less than AC needed to produce corona?
what is (+) and (-) in generator field detector stand for?
What is the function of Igniter in 250 watt HPMV street light?
where the Motorized mccb to be used? In Motor control center panel starters ,it is use full. please answer