How to calculate cable size for a particular load? i have 12
MW,11KV Motor 3 Phase, what should be cablesize?
What are the points to remember for cable sizing calculations?

Answers were Sorted based on User's Feedback



How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be ..

Answer / mahesh sali

For Cal.the cable size , pl. see the below size

1) Cal. the full loasd current of motor
2) cal. the voltage drop from ht starter panel to motor at
starting and running .
3) as per IEC rule u should take the 20% additional to ur
selected size of cable.

Base on the above step we can easily cal. the size of cable

Is This Answer Correct ?    5 Yes 3 No

How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be ..

Answer / manoj

Calculate steady state voltage drop and motor starting voltagedro they should be within limit also the short circuit withstand capacity to satisfy i2t

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

why rating of alternator in kva & induction motor in kw

9 Answers   Siemens,


What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?

0 Answers   HPCL,


what is the formula to calculate voltage drop/loss on 66KV Transmission Line?

0 Answers  


Transformer Parallel Operations

1 Answers  


what is power factor in ac ckt ?

5 Answers  






What happen while we measure the Current in Rotor?

1 Answers  


what is the term of desruptive voltage

5 Answers   Bhel, Energy Infratech,


what is current check gurd relay?

0 Answers   MRF,


Why does the DC voltage needed is less than AC needed to produce corona?

2 Answers   TATA,


what is (+) and (-) in generator field detector stand for?

0 Answers  


What is the function of Igniter in 250 watt HPMV street light?

1 Answers  


 where the Motorized mccb to be used? In Motor control center panel starters ,it is use full. please answer  

1 Answers   Voltas,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)