By Earthed system, we mean a three phase system whose star
point is grounded directly. In this case, in the event of
the earth fault, the voltage in the faulty phase will
become zero. The voltage between the healthy phases and the
ground will be the same, 11kV/1.732 or 6.6/1.732.
However, in case of an earth fault in an ungrounded system,
the voltage between the healthy phases and the ground will
be equal to the phase to phase voltage. i.e. 11kV or 6.6 kV.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / srinivasa r ao
In un earthed power supply the earth wire is connected to
the body so it gives shock when we touch the PC metallic
body.
incase of earthed systems shock will occur.
Is This Answer Correct ? | 2 Yes | 2 No |
how we select HRC FUSE ?
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
Explain Continuous and Discrete signals?
how many units consumed by 8.5 ton ductable split ac in one hour in 3 phase?
WHY WE DO NOT TAKE THE POWER FACTOR MORE NEARER TO UNITY IN AC GENERATOR?
what is 6 pulse and 12 pulse inverter? Explain brifly
how we can calculate power factor in single phase & three phase ?thank u
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
what is the difference between changer, converter and transformer?
what is GRR(Grid Rotot resistance)?Why it is used beside of LRS?
9 Answers ACC, L&T, Sri Biotech,
can we make a electric generator,which can not use any type of fuel,air,solar,gas,thermal,coal,petrol,etc and able to produce electrical energy (or self electricity generating generator)
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer