how do i calc busbar size for a rated current?
Answer / goutam ghosh
Busbar size for a rated current can be calculated from
CURRENT DENSITY. Current density for copper is 160
amps/sqcm.(1000 Amp/sqinch.)and for Aluminium the same is
130 Amp/sqcm.(800Amp/sqinch.).Say for 200 amps reated
current Aluminium busbar of cross section 30mm X 5mm or
Copper busbar having cross section 25mm X 5mm should be
used according to nearest availability at market.
| Is This Answer Correct ? | 15 Yes | 10 No |
What is the difference between UPS and SMPS?
What is resonant peak?
why the transmission side of the generating transformer is always star??
what is negative,positive abd zero sequence current explain clearly
define as synchronous generator
How we calculate the spacing between the conductors in 11,33KV lines?
Any body can help me in getting LT panel test procedure.
where to use CT and PT?
What is mean by % impedance of transformer? detail explanations expected.
what is the function of open delta System?
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
slipring induction motor starting time Lrs operating why lrs starting time lrs outer body didn't get shock
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)