how do i calc busbar size for a rated current?
Answer / goutam ghosh
Busbar size for a rated current can be calculated from
CURRENT DENSITY. Current density for copper is 160
amps/sqcm.(1000 Amp/sqinch.)and for Aluminium the same is
130 Amp/sqcm.(800Amp/sqinch.).Say for 200 amps reated
current Aluminium busbar of cross section 30mm X 5mm or
Copper busbar having cross section 25mm X 5mm should be
used according to nearest availability at market.
| Is This Answer Correct ? | 15 Yes | 10 No |
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
Define transfer function?
what is sf6 where it is use & working or function ?
Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.
What is difference between earth leakage relay and restricted earth fault relay ?
can we use NPT glands in LT panel
is it possible to flow a current between nutral and earth in a circuit? although nutral and earth having same potential diffrence? i=0/r=0A if any body now any solid reason because i am getting a triping problem in rcbo due to nutral and earth shorting???
Why have to use copper cable for local isolator to motor ?
gas turbine genrator reactances
what is the unit of current
what are the protection equipments used betbeen HT line and transformer in a power plant
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)