what is hart communicater? can u give brief explanation
about this issue?
Answers were Sorted based on User's Feedback
Answer / ajith294
Hart Communicator (Highway Adreessable Remote Traseducer)
is a communication device, which we can used for the
configuration, such as the input range (LRV, URV, Units,
Damping), if the transmitter is temperaure, we can change
the senser ( Mv / Ohms),
And trim (Lower range trim, Upper range Trim and Zero trim.
but is not a standard to use a calibrator. we must use a
high sensitive test equpments ie mA reader (Multimeter) to
read the accurate output mA
Now a days the control valve positioner also having HART
Protocol, means we can configure and put the auto
calibration of valve throgh HART Communicator.
there is no need to calibrate a HART Communicator, it is
clearly showing the user manual provided by ROSEMOUNT.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / waqar ahmed chishti
Heart communicator is a device which can sense the smart
series transmitters and also provide out put of TX and also
match it with supply of input throw this a TX can be
calibrated without multimeter and it will also adjust the
zero and span or TX with out touching the TX,Heart
communicator can also used as source to provide 4 to 20 ma
to check a loop,it also use to calibrate DVC positioner it
will provide 4 to 20 ma to calibrate positioner,
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / manohar chotrani
HART® Field Communications Protocol is widely recognized as
the industry standard for digitally enhanced 4-20 mA smart
instrument communication. The HART protocol provides a
uniquely backward compatible solution for smart instrument
communication as both 4- 20 mA analog and digital
communication signals are transmitted simultaneously on the
same wiring. HART provides many benefits promised by
fieldbus, while retaining the compatibility and familiarity
of existing 4-20 mA systems.
Analog + Digital Communication
For many years, the field communication standard used by
process automation equipment has been a milliampere (mA)
analog current signal. In most applications the milli
ampere signal varies within a range of 4-20 mA in
proportion to the process variable being represented.
Virtually all installed plant instrumentation systems use
this international standard to communicate process variable
information.Simultaneous Analog + Digital Communication
HART uses Frequency Shift Keying to encode digital
information on top of the 4-20 mA analog signal
HART Field Communications Protocol extends the 4-20 mA
standard to enhance communication with intelligent
measurement and control instrumentation. A major step in
the evolution of process control, the HART protocol is
fostering significant innovation in process instrumentation
capabilities. The enhanced communication characteristics of
this important technology are reflected in the protocol
name, HART which stands for “Highway Addressable Remote
Transducer”.
The HART protocol enables two-way digital communication
with smart instruments without disturbing the 4-20 mA
analog signal. Both the 4-20 mA analog and HART digital
communication signals can be transmitted simultaneously
over the same wiring. Primary variable and control signal
information is carried by the 4-20 mA (if desired), while
additional measurements, process parameters, device
configuration, calibration, and diagnostics information is
accessible through the HART protocol over the same wires at
the same time. Unlike other “open” digital communication
technologies for process instrumentation, HART is
compatible with existing systems.
| Is This Answer Correct ? | 2 Yes | 0 No |
Is that Speed Probe and Vibration Probe sensors are same,if yes what is the diff b/w them?
how we will install a positioner ?
When doing a liquid seal on a differential flow transmitter , most of the time the sealing liquid will be heavier then the process fluid. For wich application will the sealing liquid be lighter than the process fluid if transmitter is mounted below the process line.
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
Why we are using temperature and pressure as a reference when measuring flow of steam?
I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
How to measure Flow of air line,what is the procedure of creating DP in line to measure Flow!
what is controlling card in dcs? how u measure dcs memory?what is bus in dcs?how u know dcs speed n ehternet speed?
I am an intru engg frm pune n completing mba marketing in may 2010, what kind of profile would best suit my educational qualifications??? Also, i will move to US in jan 2011, so this job experience should count Over there too 'coz i want to continue workin even there....
what is the difference about HART, and 4-20mA signal?
What is upsampling and downsampling?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)