What is the advantage of Neutral graunding transformer
insted of Neutral graunding Resistance in generating
station explain briefly.
Answers were Sorted based on User's Feedback
NGR and NGT serves the same purpose of limting the earth
fault current to the rated values which basically depends
upon the core damage curve of generator. Differece is NGT
gives earth fault protection of 100 % winding whereas NGR
protects only 95% of the generator winding. Potential
difference of the 5% winding (towards neutral) with respect
to neutral is very less so the earth fault in that region
of the winding is not sensed. This is avoided in NGT using
sensing of 3rd harmonic under voltage based principle in
secondary of the NGT.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / devang machchhar
with the same value of resistance, NGT shows more
resistnace in ground circuit and limit the current for
instantanious high fualts at the first 3 power cycles,
providing safety to the generator or transformer.
| Is This Answer Correct ? | 0 Yes | 2 No |
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
Why servomotor and induction motor are in different shape
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Dear all i am kumaravel. now in chennai. my work is control and relay panel auto cad designing.up to 11kv to 400kv then question is i am improving my knowledge. i want some books name and auther are available for this C&R panel related. plese any one help me
What kind of test is conducted commonly for generator? And explain briefly
what is the meaning of Dd0yn11
what questions will be asked for 11/33KV licence interview APSEB hyderabad. Can any one share question and answers.
Which of the following are ill suited for energy efficient motors application?
What will happend if given Vfd out put to step up transformer
Dear sir,how should i set the relay in star delta starter..say ex i am having 4ohp motor,,wht should be the relay setting...?
Hi I'm doing my MBA(3rd semester).I applied for the post of ET conducted by BHEL the last year.I cleared the written and lost in personal interview.Again I wrote the exam this time and cleared the written n yet to take the personal interview.Shall I disclose in the interview about my studies.What shall i say if they ask about my change from studies to job
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)