What is the advantage of Neutral graunding transformer
insted of Neutral graunding Resistance in generating
station explain briefly.
Answer Posted / amit khamesra
NGR and NGT serves the same purpose of limting the earth
fault current to the rated values which basically depends
upon the core damage curve of generator. Differece is NGT
gives earth fault protection of 100 % winding whereas NGR
protects only 95% of the generator winding. Potential
difference of the 5% winding (towards neutral) with respect
to neutral is very less so the earth fault in that region
of the winding is not sensed. This is avoided in NGT using
sensing of 3rd harmonic under voltage based principle in
secondary of the NGT.
| Is This Answer Correct ? | 3 Yes | 2 No |
Post New Answer View All Answers
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
What type of DC motor would you see for a lift?
How to calculate wire length,size & current? ( related to control panel)
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
An ISP is granted a block of addresses starting with 150.80.0.0/16. The ISP wants to distribute these blocks to 2600 customers as follows. a) 200 medium size businesses; each needs 16 addresses b) 400 small businesses; each needs 8 addresses c) 2000 households; each needs 4 addresses Design the subblocks and give the slash notation for each subblock. Find out how many addresses are still available after these allocations.
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
what is the minimum voltage require to injure our body?
why do motors burn out? I understand why adding parallel loads to a power source means more current moves through the circuit, and can destroy circuit elements by overheating. What about when you have a vaccuum cleaner intake flush against a floor, a room fan sitting directly against a wall, or a power drill trying to drill through something too hard?
how to measure earth resistance of a substation
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
1.how many earth pits are required for 1000 k.w plant include substion , transformer ? 2. how many earth pits are required for 500kva generator.what is formula to calcute?
what is distribution board?
what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)
Define filter?