Answer / s c budhiraja
(1) First for star connections:line
current=1000/.75*1.73*.75*440=1.75 A for both line &
phase.
(2) For delta connections; Line current=1.75A
Phase current=1.75/1.73=1A
Note: There no use of Motor efficiency here.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / michael
NOTE : YOU NEED MOTOR EFFICIENCY
BECAUSE IF THERE IS A RATING GIVEN
IN TERMS OF KW. IT IS ALWAYS THE
OUTPUT POWER OF THE MOTOR..
SO WEE NEED TO CONVERT IT TO
INPUT POWER IN ORDER TO COMPUTE THE
CURRENT.
Is This Answer Correct ? | 4 Yes | 0 No |