I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency
75%(star delta connection)Motor. How to calculate line
current & Phase current (1) Star connection (2) delta
Connection
Answers were Sorted based on User's Feedback
Answer / s c budhiraja
(1) First for star connections:line
current=1000/.75*1.73*.75*440=1.75 A for both line &
phase.
(2) For delta connections; Line current=1.75A
Phase current=1.75/1.73=1A
Note: There no use of Motor efficiency here.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / michael
NOTE : YOU NEED MOTOR EFFICIENCY
BECAUSE IF THERE IS A RATING GIVEN
IN TERMS OF KW. IT IS ALWAYS THE
OUTPUT POWER OF THE MOTOR..
SO WEE NEED TO CONVERT IT TO
INPUT POWER IN ORDER TO COMPUTE THE
CURRENT.
| Is This Answer Correct ? | 4 Yes | 0 No |
what is star&delta connections?
what is the meaning of 0.5ohm Resistance
Transformer calculation
1 Answers Aramco, LMW Lakshmi Machine Works Limited,
What is difference between Harmonic and Non harmonic Capacitor Bank?
what is thermo stat, explain how its working?
A 40 kva transformer has a core loss of 400W and a full load copper loss of 800W. What is The proportion of full load at maxmimum efficiency?
ups and invertor battery selection chart and full formula
How to take vector group test for Ynd11 transformer.
Differenciate between circuit wiring and sub main wiring with illustrations
enlist types of dc generator
pls send me some question and answer for rrb railway interviw related 2010
What are the types of control system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)