Answer / s c budhiraja
(1) First for star connections:line
current=1000/.75*1.73*.75*440=1.75 A for both line &
phase.
(2) For delta connections; Line current=1.75A
Phase current=1.75/1.73=1A
Note: There no use of Motor efficiency here.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / michael
NOTE : YOU NEED MOTOR EFFICIENCY
BECAUSE IF THERE IS A RATING GIVEN
IN TERMS OF KW. IT IS ALWAYS THE
OUTPUT POWER OF THE MOTOR..
SO WEE NEED TO CONVERT IT TO
INPUT POWER IN ORDER TO COMPUTE THE
CURRENT.
| Is This Answer Correct ? | 4 Yes | 0 No |
explain LED lamps?
Why should we hire you over the others waiting to be interview?
does not the circulating current in a transformer affect the flux distribution in the transformer core
Latching current is slightly less than ?
what is mean by NTPC?,why didn't electric shock in train?
What is the definition of ohms law?
7 Answers AZ Engineering, Ecil,
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
What are the advantages and disadvantes of delta and star connections in transformers and alternators?
what is the voltage equation of 240/12 v transformer??
why rating of motor in HP?
how the phase convertor changes the no. of phases
Why capacitor bank ratting Kvar?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)