i want to know about for what reason we are using star
delta starter? how it works? what are the advantages?
Answers were Sorted based on User's Feedback
Answer / prashant kaushik
Star Delta use for starting of motor as during starting
motor take high current so we can reduce it through using
star delta starter.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit agrawal
star delta starter are used for controlling starting current. as we know, when we start any motor/pump then motor takes 6 times if rated current as there is no back emf ins tarting(speed zero).
If we apply star circuit then the voltage will be one third of delta circuit, in the same way current will be reduced.
This is the answer.
One more thing that all the HT(6.6KV) motors also be in star to control the starting current and to save the cost of insulation for both motor and connected cable.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kishor
starters are used for the purpose of to reduse the starting current...
in star-delta starter motor starts in star connection at this time motor voltage reduses than 1/root3...
there fore current is also reduse 1/root3...
and after some time motor is automatically convert to delta mode through timer....
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / prabhakar
Stard delta starters are to avoid accident it works with
contactors it save energy.
do you want to know what is star delta
the motor whih has dol connection will consum more current
and the motor which as star connection will consume less
corrent that is the reson we use motors and star delta
starters
Is This Answer Correct ? | 0 Yes | 8 No |
what is PDU in transformer?? which company manufacture??
Can you explain about Restricited earth fault protection scheme
Whta is WT in a transformer, specify its function.
how the rotating magnetic fieldis produced in induction machines??? give the correct explanation.is there any mathematical expression for the same?
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
Which transformer is suitable for 220/11 kV, 60 MVA, distribution , Y-Y or D-Y or Y-D, give comparison for the same.
how the synchronizing is obtained at bus couplers in grid substation? (because there we cannot change the frequency in one of transmission lines like in generator synchronization)
How to Calculate the current drain in the battery (1.4V) for the 2mins time period?
what is basic difference betmeen normal & flame proof motor??
Can we install and run MCCB suitable for 440v 3Phase 4wire system, on a 220V 3Phase 4Wire System.
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?