i want to know about for what reason we are using star
delta starter? how it works? what are the advantages?
Answer Posted / amit agrawal
star delta starter are used for controlling starting current. as we know, when we start any motor/pump then motor takes 6 times if rated current as there is no back emf ins tarting(speed zero).
If we apply star circuit then the voltage will be one third of delta circuit, in the same way current will be reduced.
This is the answer.
One more thing that all the HT(6.6KV) motors also be in star to control the starting current and to save the cost of insulation for both motor and connected cable.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
magnetizer priciple
What is the Resposiblity of Electrical Utility Engineer
What is the function of interposing current transformer?
What is an iron loss or core loss pi?
what are all the components required to assemble solar panel other than pv cell?
how to protect motor in dol starter having capacity of 30 hp.40 hp?
What are the operation carried out in thermal power station?
sir, Is their any measuring unit of knoking? please explian?
why the name trunking bus PT
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
difference between a diode and thyristor?
How LT megger works ?
what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye