how can we find a burden of potential transformer? what
does it effects? how can we calculate rated load of it?
Answers were Sorted based on User's Feedback
Answer / raghavendran
Burden CAn be denoted in VA or in Ohms.Consider that to a PT
secondary we have a relay connected to it.Now the Total
impedance on the PT secondary is given by Zt = Zsec + Zlead
+ Zrelay.where the Zsec is the impedance of the PT
Secondary,Zlead be the impedance of the lead between the PT
secondary and the Relay,Zrelay be the Impedance of the relay.
Now from the VA capacity of the PT,under normal operating
condition of the PT,calculate the secondary current, Isec.
burden interms of VA can be obtained as Zt*Isec.
Burden interms of Ohms can be had from - Rated
VA/((Isec)*(Isec))
As Burden increases beyond the prescribed value, the
accuracy decreases below the allowable value.
| Is This Answer Correct ? | 30 Yes | 2 No |
Answer / tuktuk
Dear Mr.Raghavendran,
Thank you for your answer, I have the same problem but after reading your answer I still have some concerns.
I am really confused. In this case, we do not know the rated burden of the VT. Now we have to calculate the total burden and then selecte the rated value from IEC standards.
__Ztotal, which you mentioned above, is in Ohm or VA?
__Zsec and Zrelay we can get the value from manufacturer but Zlead, is it calculated by this formula: Zlead= (p*L)/S
(where: p is specific resistivity of copper in ohm.mm^2/m; L is length of lead between the PT secondary and the relay in meter; S is the section of lead in sqmm)? Is this true?
__I dont know how can we get secondary current Isec? (I guess Isec=Usec/Zt, isn't it?)
__And Burden in VA = Zt*Isec. As Ohm law, we have P=VI=RI^2=U^2/R, I do not understand the formula that you used to calculate Burden of VT in VA
Hope that you could help me to solve this stuck in my head.
Thank you.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuktuk
Dear Mr.Raghavendran,
Thank you for your answer, I have the same problem but after reading your answer I still have some concerns.
I am really confused. In this case, we do not know the rated burden of the VT. Now we have to calculate the total burden and then selecte the rated value from IEC standards.
__Ztotal, which you mentioned above, is in Ohm or VA?
__Zsec and Zrelay we can get the value from manufacturer but Zlead, is it calculated by this formula: Zlead= (p*L)/S
(where: p is specific resistivity of copper in ohm.mm^2/m; L is length of lead between the PT secondary and the relay in meter; S is the section of lead in sqmm)? Is this true?
__I dont know how can we get secondary current Isec? (I guess Isec=Usec/Zt, isn't it?)
__And Burden in VA = Zt*Isec. As Ohm law, we have P=VI=RI^2=U^2/R, I do not understand the formula that you used to calculate Burden of VT in VA
Hope that you could help me to solve this stuck in my head.
Thank you.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / santhoshkumar
Hello Mr.Raghavendran CT purpose to reduce the current rating of the system to measuring purpose and The Sy will be opened they will higher current carrying capacity in SY so conductor size will be high and step up high high voltage generate higher harmonics it will create serious hazardous in CT CKt
| Is This Answer Correct ? | 2 Yes | 8 No |
our industries ht line so power fluctation(once drop of power please rectify causes
what will be the magnetizing current in the testing of 27 MVA transformer?
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
Period of infinite continuous fourier series a. N b. N+M c.infinite
what is the order of mgnetiation current in a current transformer of 1000A/1A ratio?
WHAT IS THE REASON FOR THE GROUND PIN IS BIGGER IN SIZE COMPARING TO OTHER PINS?
can we use existing 6300V alternator for generating 6600V by increasing excitation,what are advantages & disadvantages to alternator & motors of 6600V.
What will happened if the neutral of the (star connected secondry) Xformer disconnected? (if its Above KVA rated one)
On what principle reluctance motors work?
types of motor starter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)