no EB power DG is not starting?
Answers were Sorted based on User's Feedback
Answer / prashant
Check if the DG is starting . If not check ur AMF panel and
the corresponding relay
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / selvan
which mode DG set connected?
manual mode- 1.battery terminal or its cable demaged.
2. low volt in battery.3. self motor problem.
4.fuel block.
auto mode- 1.EB power failure comand not going to dg
control panel. 2. DG CONTROL panel not reset.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraj.m
this is fully interlock system so this is not working in eb
power dg is not starting
| Is This Answer Correct ? | 5 Yes | 2 No |
if the DG is in auto mode
1)Signal may be not reaching the DG from main panel.
2)Battery may not have enough charge to crank the DG.
3)Shortage of fule in DG or flow of fule to th DG may have
problem.
4)In case of more no of DG controle wiring may have problem.
5)synchronization off DG may have problem.
6)phase sequence may have problem.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sreekanth
plz check the battery of dg.if it is totally discharged
then dg will not start
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / elangkumanan
dg set battery discharging problem.
auto mode sanner not working.
fuel was low.
radiator water level was low.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is meant by earth fault and how it happens....
In Energy meter How many rotation Equal to one unit.
what will hapen if we give ac supply to dc motor?
when secondary volts is given how do we find primary volts, turns, amps of primary and secondary given???
what is the size(sq.mm) of these conductors dog,rabbit,tiger,panther,mush,
In power point wiring,often,we use less size of earth wire compared to phase & neutral wire and we use big size pin in pug top. how is it justified? can we use small size cable for earthing?
what is earth-fault?when it occurs? to check where it occurs what type of test should we do?
give me battery AH calculation in U P S
What is the difference between diesel generator engine with and without turbo charger with the same capacity?
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)