I saw one P&ID 6" control valve has been connected with 8"
process line, and 2" valve also connected in parallel with
6" valve. why the 2" valve connected in parallel, Is there
any technical reason. please clarify. With Regards-Kittu
Answers were Sorted based on User's Feedback
Answer / chowdary
The controller name is Split Range controller.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / divyang
There can be many reasons to provide two CV-
1. Case where flow controllability is extremly important.
Hence to get better control at lower load 2" CV will be
operated & once plant reaches cerain load higher size
control valve comes into picture.
2. Higher size CV is kept on certain value of manual
opening, and fine control is done by smaller valve. eg if
flow requried is 10000 kg/hr and controlling limits are +/-
200 kg, smaller CV will give fine control.
3. During revamp of the plant capacity instead of
increasing the existing CV, if a samller size CV is
available in spare same can be installed in parallel
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / guest
any technical reason. please clarify. With Regards-Kittu
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ajith294
above answer is split range controller. what is a split
range control? two control valves are controled by a
controller is split range. for eg: 50% of controller out
put both of the valve will be close condition , see below
table.
% input Valve A opening %, Valve B opening&
0 0 100
25 0 50
50 0 0
75 50 0
100 100 0
but in your question on 2" valve is connected parrallel
with 6" Control valve. means for the bypassing 6" control
valve, they are using 2" valve.
for technically it is very very improtant. becasue at the
time of maintance of the control valve, there will be no
disturbance in process.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / girishkumar
It is called split range control and split a big CV into two
parts as 1:4 for fine control.ie:- in 0% both valves keep in
close. In 25% the 2" valve keeps fully open and 6" keeps
fully close. In 50% the 2" keeps fully open and 6"keeps in
25%open. In 75% the 2" keeps fully open and 6"keep 50% open
and in 100% both keeps fully open.These two valves
controlled by same controller with two AO.
| Is This Answer Correct ? | 0 Yes | 0 No |
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
how many types of preheaters are in cement industry & what r they can any body explain?
how u choose thermowell lenght n pnumatic C/v size?
what is the difference between single and double compression cable gland
What is MLFB number for Siemens?N How they are defined?Give me Answer with example like take any Signal module....
What are different type of instrument cable
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
what is the difference about HART, and 4-20mA signal?
Determine the manipulated variable, controlled variable, and the measured variable given a description of various typical industrial processes.
What is Actuator?
Explain about signal isolator
what is control valve and how is work
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)