WHAT SHOULD BE THE RATING OF generator required to run a
pump motor of 45 Kw.
Answer / sachin kusumkar
KW = KVA*PF,
45KW = KVA*0.8
KVA = 56.25
Considering DG Efficiency 80% of rated KVA=56.25*1.25=70
cONSIDERING 20% SPARE /FUTURE LOAD KVA=70*1.2=84
so you need to select nearby available rating for selected brand in the market.
Is This Answer Correct ? | 11 Yes | 1 No |