Answer / raghavendran r
The reverse power relay is used to monitor the direction of
power from A.C generators, if the current in the system
being monitored is reversed, to a value greater than the
customer adjustable preset limit the relay will energise.
The adjustable trip point is 2% to 20% of input current. An
adjustable time delay of 0 to 20 seconds is provided.
Correct setting of the trip point and time delay, will
ensure protection against motoring action of the Syn gen.
An inadverdent relay is used to trip the circuit when a syn
gen has been energised or excited inadvertently.
Is This Answer Correct ? | 1 Yes | 0 No |
what is subtransient , transient and study state ac components
why we are calculating the capacitance between phase(conductor line)and ground in transmission line?why cant we calculate capacitance between the phase and the nuetral line?if so what is procedure.
what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me
HOW TO CALCULATE AMPs OF CURRENT TRANSFORMER IN HT Panel
good morning sir, can u please tell me what type of questions asked in jindal so i can do my best in exam.
Essential condition for parallel operation of two single phase transformer is that they should have same A polarity B kVA rating C voltage ratio D % impedance
Type of cable insulation?
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?
in short circuit. test of a transformer 5 to 10% ofvrated voltage is used why??? if we use rated voltafe then what will be?
electricity bill multiplication factor 487.20xconsumption=total unit in kwh. what is 487.20 ?
what are the values to be accepted on 3 core 185sq mm for 11000volts on insulation resistance between conductors and between conductors and earthed?
What is water cooled chiller plant?