what is the formula for calculating milliampere at different
pressure points for eg 4-20 ma = 3-15 psi but if i have to
check the ma at 4.6 ma?
Answers were Sorted based on User's Feedback
Answer / lalchhotex
as per as nick formula it is not fullfill anoter range like
as 0-100 for level, 0-14 for PH
formula is
16*(unknow value-Low end of rang)
mA O/P = 4+ ---------------------------------
transmitter span
Suppose range is 3-15 PSI according to question what is the
psi for 4.6 mA
by the formula
4.6-4 =16*(unknow value-3PSI)
----------------------
12 PSI
0.6*12PSI
--------- = (unknow value-3PSI)
16
7.2 psi
------- = (unknow value-3PSI)
16
0.45 psi = (unknow value-3PSI)
0.45psi+3psi = unknow value psi
3.45 PSI = unknow value psi answer
| Is This Answer Correct ? | 23 Yes | 2 No |
Answer / gunasekaran
4~20mA=3~15psi
4.6mA=?psi
psi =(mA -mA Zero)/(mA Span)×Range Span+Range Zero
4.6-4
psi = ------ x 12+3
16
0.6
psi = ---- x 12+3
16
psi = 0.0375 x 12+3
psi = 3.45
4.6mA = 3.45psi
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / abdulbasit137@hotmail.com
this is the one of the best formula for this situation
measuring value (1) - low ranmeasge value (1)/span
=
measuring value (2) - low range value (2)/span
u know span high value - low value 4 to 20 span is =16
3 to 15 span is = 12
simple
mv1 - lrv1 = mv2 - lrv2
span span
4.6-4/16= ?-3/12 = 4.3psi ans
| Is This Answer Correct ? | 1 Yes | 13 No |
in transmiters(rose mount) how to check output 4-20ma ? and input 24v? i need exact explanation?
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
why need 3 element system in power plant? if it is not there then what l happen?
In a ball valve which require 24v dc supply to operate, whose solenoid valve doesn't have any + or - indication, how can we make wiring connectionto solenoid valve?
1 Answers Process Control Technologies,
in plc source and sink meaning?
regarding level tx i would like to know how to select the range of the level transmitter in a closed drum(steam drum or deaerator)?
, Instrument Index, P&ID review, I/O schedule, datasheet, DCS / Analyzers specifications, loop diagrams, hook-up drawings.
Regarding MOS (maintenance override switch), I want to know its function and its state ( 1 or 0 when not activated ). An example will be very helpful..thank you.
in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?
role of electrical engineer in the instrumentation industry
What is the use of control cable?
please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)