my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
Answers were Sorted based on User's Feedback
1) Most likely, the 4-20mA scaling (what the 4-20mA represents) is not the same on the transmitter as it is on the DCS.
The scaling has to match, that is, be the same on both the transmitter and the DCS analog input.
2) A ground loop will cause an offset. The offset can be negative or positive, depending on the polarity of the ground loop.
Eliminating ground loops can be a major task, so most times, a loop isolator is used to isolate the transmitter from the DCS, which eliminates the ground loop.
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shahid
Carl Ellis is give the good answer that is the technical error that may occur but some time there is possibility of miss matching in the range of DCS & the field transmitter.That's why should check the both ranges of URV-LRV.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheshrp
Reason of DCS and field equipment range different so dcs and field variable reading
So dcs & field range same as problem your solve
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raghubir nishad
Range Can match in Field instrument or PLC/DCS both side.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between DCS and SCADA?
How will you calibrate an interface level trol/normal level trol in line and in w/s?
What is the PLC Level & type.
2 Answers Bhushan Power Steel,
How to interfacing microcontroller with a DC motor
Briefly describe instrumentation job
what is difference between hart signal and analog signal (4 to 20 ma)
Condensation within a sight glass? Would you expect there to be more problems when using a sight glass if there is condensation on the inside or the outside of the glass, and why?
Is there’s power on the bus (if so, state whether on the signal bus, or on a separate in the following: a) HART b) Profibus DP c) Profibus PA d) DeviceNet e) Foundation Fieldbus
how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?
1.what is beta in control valves? 2.what is the condition followed by light in LASERs? 3.1kg/cm2=?psi 4.Integral action reduces what? 5.about vena contracta 6.a simple RC circuit 7.thermistor material's temp coefficient of resistance 8.if wave passes through the thicker area of a chord to a thinner area what changes will occur to wavelength? 9.if 4-20 mA represents 0-10 kg/cm2 what will be the current when pressure is 5 kg/cm2.................
why two probes are used in turbine flowmeters?
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?