my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
Answers were Sorted based on User's Feedback
1) Most likely, the 4-20mA scaling (what the 4-20mA represents) is not the same on the transmitter as it is on the DCS.
The scaling has to match, that is, be the same on both the transmitter and the DCS analog input.
2) A ground loop will cause an offset. The offset can be negative or positive, depending on the polarity of the ground loop.
Eliminating ground loops can be a major task, so most times, a loop isolator is used to isolate the transmitter from the DCS, which eliminates the ground loop.
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shahid
Carl Ellis is give the good answer that is the technical error that may occur but some time there is possibility of miss matching in the range of DCS & the field transmitter.That's why should check the both ranges of URV-LRV.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheshrp
Reason of DCS and field equipment range different so dcs and field variable reading
So dcs & field range same as problem your solve
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raghubir nishad
Range Can match in Field instrument or PLC/DCS both side.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is lead lag compensator and for wat v using that???
can i get model question papers of mahagenco exam?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
For an Instrumentation Engineer, is there any effect on Instruments of safety zones like zone0, zone1, zone2. As an instrumentation Engineer, what we have to consider or remember while working in these areas.( zones 0,1,2).
What is motion balance principle?
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
What is the processor scan time of allen bradle control logix processor 5555 lenin lenin123us@rediff.com
why we cant transmit the dc current easily
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
How do you measure g's?
5 Answers Aramco, GNFC, HPCL, Polmon, Thermax,
what is the procedure of belt scale calibration?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)