my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
Answers were Sorted based on User's Feedback
1) Most likely, the 4-20mA scaling (what the 4-20mA represents) is not the same on the transmitter as it is on the DCS.
The scaling has to match, that is, be the same on both the transmitter and the DCS analog input.
2) A ground loop will cause an offset. The offset can be negative or positive, depending on the polarity of the ground loop.
Eliminating ground loops can be a major task, so most times, a loop isolator is used to isolate the transmitter from the DCS, which eliminates the ground loop.
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shahid
Carl Ellis is give the good answer that is the technical error that may occur but some time there is possibility of miss matching in the range of DCS & the field transmitter.That's why should check the both ranges of URV-LRV.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheshrp
Reason of DCS and field equipment range different so dcs and field variable reading
So dcs & field range same as problem your solve
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raghubir nishad
Range Can match in Field instrument or PLC/DCS both side.
| Is This Answer Correct ? | 0 Yes | 0 No |
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
Why trim span ? How?
How does milli volt is created in themocouple?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
what is the standard of determining opening/closing time of Motor Operated Valve?
What is hook's law
what is the difference between transmitter and smart transmitter ?
if we have 450 mm heigth boiler drum level ,so what is span & zero value for a dpt tranmitter
tell about various protocols used in different plcs
Draw a simple circuit for a well head control panel used to protect the well against fire, leak, blockage, ESD, & controls the operation of one downhole & one surface safety valve. Explain the operation and controls
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)