why capacitor bank is not used in generator power
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
When the generators(gen) are connected to grid or net work
,if all the gens are run at unity pf ,there will be drop in
voltage due to inductive load in the system as the current
increases.Then to maintain system stability, LDC requests
large generating stations to increase the voltage . This
will increase the KVAR and results in lower lagging pf in
the gens. That is why the gens are designed for 0.8/0.85
pf.The pf of gens can be kept at any value by varying
excitation or resetting in APF mode.As pf control is
required by generating stations,capacitor banks are not used
.Capacitor banks can be used in the system to reduce the
inductive load but not in the gen stations.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / k.prakashchandra
Pf of generator can be brought to required value by varying
excitation.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / k.prakashchandra
If the gen is connected to grid ,its pf can be regulated by
varying the excitation or by APF mode.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / umkesh
One more question can be use Capacitor Bank in Aux consumption panels in Thermal Power plant like CHP
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
In the line 9, read as ' As pf control is not required'.
| Is This Answer Correct ? | 1 Yes | 4 No |
What are types of losses in the Transmisson Lines ?
Motor also having losses, we call KW rating. In transformer and generator having losses but we call KVA Rating why?
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
No load efficiency of transformer is ___________ than full load efficiency
What is defference between earthed and unearthed cable(HT)? Which is better for under ground cabling?
why needtwo winding LV and HV in transformer?
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
Is voltage & potential transformer are the same? Are they used for same application ?
my self i am raghu working as tech.. in my college the maximum demand is 211 kva presently we are using 12kva capacitors the target power factor is .95 so what capacity of capacitor banks should i install
for flour light (garden light) how much deep need to put 222ov 0
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)