If R and Y terminals are short circuited,then power will
cut. we all know that power cannot be stored.what will
happen to already generated power at power station?
Answers were Sorted based on User's Feedback
Answer / hm
when L-L fault occurs, electrical power Pe (generated by
alternator) becomes zero but mechanical power Pm (turbine
giving to alternator) remains as it is i.e. Pm > Pe. so
alternator tries to retain its stability(see power swing
curve for details) by deaccelerating rotor(up to synchronous
speed).if area under acceleration is equal to area under
deacceleration machine retains its stability else protecting
relay trips the machine.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / senthil
SHORT CIRCUIT MEANS CURRENT HIGH .IT DAMAGE THE EQUIMENT
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / guru
The Generator runs on less load (Means Less current) and
the power is not generated to its full capacity.
| Is This Answer Correct ? | 1 Yes | 2 No |
What happens to an electric motor if it has poor or no ventilation. Will it burn out? If it will, how long it will run before it burn out?
What is the significance of integral controller and derivative controller in a pid controller?
what is the transformer
why most of the modern day type electrical appliance have 2 pins rather than 3 pins?
what is difference between the buscoupler and bus raiser?
What is the formuala to calculate the rating of motor protection circuit breaker
what will happened to give the dc supply to ac transformer?
What do you mean by dependent and independent voltage sources?
Is there a possibility to use such a treshold voltage for the NMOS part of a CMOS circuit that during the switching it will start conducting only after the PMOS part will be already closed, by this eliminating the leakedge current? Please note, I'm not asking about the well bias in standby mode, but about the "antileakedge" measures during normal operation.
What is a Single Phase and Three phase Power? How it will be converted or transformed into another form?
what can be the causes of capacitor start motor having a higher current that its actual
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)