Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate KW saving for power factor correction from
0.92 to 0.98 at 350KW load?

Answers were Sorted based on User's Feedback



How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?..

Answer / m p narayanan

The question is about the KW saving if pf is improved from
0.92 to 0.98. Answer #1 is silent on the KW saving, but
logically says that 80 KVAR is needed for the pf
improvement (say, by installing a local capacitor bank).
Here , there is a calculation mistake. The value should be
77.99 KVAR instead of 80 KVAR.
Answer #2 also has calculated the same thing and wrongly
declared that it is the KW saving.
The fact is that there is no direct saving in KW by
improving the pf. If 350 KW is needed by the load, it has
to be supplied by the grid. Pf improvement is done for
reducing the KVAR requirement from the grid, not the KW. A
350 KW load at 0.92 pf takes 149.07 KVAR from the grid
whereas the same load of 350 KW at 0.98 pf takes only 71.08
KVAR from the grid, the difference of 77.99 KVAR is
generated locally by the Capacitor bank. The corresponding
KVA at 0.92 pf and 0.98 pf are 380.43 KVA and 357.14 KVA
respectively.
The industries install capacitor banks to improve the pf
with the specific intention of saving electricity bill
because power utilities have a two part tariff – part-1 for
the maximum demand (ie; KVA) and part-2 for the KWH
consumed. This is necessary because the line current is
directly proportional to the KVA and hence the overhead
line conductor size, KVA rating of the transformers
upstream, size of the circuit breakers etc. are dependent
on this. The less the line current, the less will be the
transmission losses. Saving in KW is the result of
reduction in line losses. Hence, as indicated above, there
is no direct saving in KW on account of improvement in pf,
but indirectly the power utility company save KW by
reducing the line losses and also, they save money by
investing less on the size of transformers etc. The quantum
of saving depends on the resistance of the transmission
line, resistance of the transformer windings etc. Hence it
can not be calculated with the available data given in the
question.

Is This Answer Correct ?    5 Yes 0 No

How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?..

Answer / pillay

if the load is 350kw at o.92 and also at 0.98 than there is
no kw saving unless you are talking about the losses you
reduce as what Mr MS Narayanan has mentioned.

Is This Answer Correct ?    2 Yes 0 No

How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?..

Answer / joel q.

You need to connect a power factor corrector and the size
of the capacitor is 80KVAR.

350tan23 - 350tan11 = 80KVAR

Is This Answer Correct ?    3 Yes 2 No

How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?..

Answer / engr mimkhan

IF your system losses is 5 %
Then loss reduction =1- (squr(.92)/squr(.98))
=0.13
=0.13 x 0.05 (5%)
=0.0065
Thus saving in kw =0.0065 x 350
=2.27 kw
This is your saving if system losses increase than kw saving will also increase..
Note squr mean Squre not root.

Is This Answer Correct ?    1 Yes 1 No

How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?..

Answer / adil naseem(pakistan)

cos(pi1)=0.92 //old power factor
cos(pi2)=0.98 //desired power factor
the forlmula for saving of Kw is:
total Kw= 350kw



Saving KW = total kw * (tan(pi1) - tan(pi2))
=350 * (0.4259 - 0.203058)
=77.9947Kw is the answer!(100% correct)

Is This Answer Correct ?    8 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

how can we Increase the Value Of Frequency in electric circuits

0 Answers   HMK,


Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?

0 Answers   HSL,


How to calculate the cross section area for a 350 m cable, motor power is 26 kw???

1 Answers   Orient,


Why diversity factor are applied to the load?

2 Answers  


The capacitive reactance of a capacitor of 1/(2(PI)) F at 10^3 H is

0 Answers  


what is the difference between the diode and the rectifier

17 Answers   Avalon, L&T, Mahacol Trexim,


what is self commutation how a thyristor discharges through a capacitor and inductor

3 Answers  


what is difference between co-generation and captive power plant?

3 Answers   TATA,


Differentiate between ideal and non ideal current sources?

0 Answers  


How could a garment factory benefit from renewable energy

0 Answers  


Mention the disadvantages of low power factor?

0 Answers  


What is Servo Ventilated Motor?

0 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)