for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
Answers were Sorted based on User's Feedback
Answer / parth belani
Since the neutral of the star connected secondary is
already grounded through NER, there is no need to run a
neutral cable.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ramesh
there is no need of taking neutral point unless u need.Because mostly in 33kv Switch board you will feed 33/11Kv or 33/6.6Kv Transformers ,which will be mostly in (Dyn11 ior Dyn1) or to any other 33KV boards. Any how you are not going to take any motors load directly in 33kv.so it s not neccessary. but if you feed any star connection load in Primary you need to take neutral point.
| Is This Answer Correct ? | 0 Yes | 0 No |
It is not necessary to run a neutral cable as the same is
not requried for a 33 kV 3 wire AC system. But you need to
be cautious about the circulating/eddy current (since in
is a single core cable) which flows through the screen of
the 33kV cable. The voltage genrated by the circulating
current should be more than 130 V as per IEC standards. In
case of heavy circulating current the cable would get
heated up. You may do earthing of the cable only at one end
and leave it open at the other end. In case of a very long
cable with joints in between, mid point bonding is
suggested.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / indreswararo kota
for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
| Is This Answer Correct ? | 0 Yes | 2 No |
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
What is the relation between the Peripheral speed(N) , no.of poles(P) and diameter(D) of a cylindrical rotor alternator ?
What are high pass filter and low pass filter? and What are the flowmeter ?
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
What do you mean by per capita requirement of electrical energy in india
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
block diagram of 2 ups system connected in parallel mode?
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
What is an ac motor?
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
In a distribution system,having 3phases & 1 nuetral.ecah phase to neutral is 230V,line-line voltage is 440V,but what is the voltage of each line.but it should obey the KVL law.
What is on delay and off delay timers
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)