Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???

Answers were Sorted based on User's Feedback



for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable i..

Answer / parth belani

Since the neutral of the star connected secondary is
already grounded through NER, there is no need to run a
neutral cable.

Is This Answer Correct ?    7 Yes 2 No

for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable i..

Answer / viki

what is NER?

Is This Answer Correct ?    1 Yes 1 No

for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable i..

Answer / ramesh

there is no need of taking neutral point unless u need.Because mostly in 33kv Switch board you will feed 33/11Kv or 33/6.6Kv Transformers ,which will be mostly in (Dyn11 ior Dyn1) or to any other 33KV boards. Any how you are not going to take any motors load directly in 33kv.so it s not neccessary. but if you feed any star connection load in Primary you need to take neutral point.

Is This Answer Correct ?    0 Yes 0 No

for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable i..

Answer / pichumani

It is not necessary to run a neutral cable as the same is
not requried for a 33 kV 3 wire AC system. But you need to
be cautious about the circulating/eddy current (since in
is a single core cable) which flows through the screen of
the 33kV cable. The voltage genrated by the circulating
current should be more than 130 V as per IEC standards. In
case of heavy circulating current the cable would get
heated up. You may do earthing of the cable only at one end
and leave it open at the other end. In case of a very long
cable with joints in between, mid point bonding is
suggested.

Is This Answer Correct ?    1 Yes 2 No

for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable i..

Answer / indreswararo kota

for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

If we know the load for generator in KW then how it will be change to amps and also if we know the load in amps how it will change in KW and what Generator is good for that...suppose load is 500 amps 3phase......??

1 Answers  


what will be happen if we apply D.C supply to the transformer

14 Answers   CCBPL,


Dear All please ive me ur ideas... What is the major diff between cu conductors and Al conductors ?

3 Answers   MX Technology,


WHAT IS THE MEANING OG (li = 7 In)

0 Answers  


how to calculate relay rating for 50kw load

1 Answers   JNU,


why are u join ntpc

0 Answers   NTPC,


What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?

0 Answers  


If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?

0 Answers  


if we supply to secondary winding how transformer work?

2 Answers  


how many load we can take for lighting

0 Answers   ABB,


what is mean by dual digital protection in the relay field?

0 Answers   ABB,


How to check phase R,Y,B

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)