What is the formula to calculate the rating of a thermal
over load relay
Answers were Sorted based on User's Feedback
Answer / barkha jha
At starting motor draws current 5 to 6 times of the flc so
overload relay setting is done this kept on mind.for e.g
3.7 kw motor the
FLC is 8 amps. we can select the relay 6A-10A range.
tripping setting is 90 % of FLC
Is This Answer Correct ? | 38 Yes | 7 No |
Answer / jayakumar.k
There is no General formula .but the general practice is
motor FLC should be the setting . for e.g 3.7 kw motor the
FLC is 8 amps. we can select the relay 6A-10A range. 8Amps
shoud be the trip setting.
Is This Answer Correct ? | 25 Yes | 17 No |
what is the difference between gsm and cdma??
why the no.of slots in stator in not equal to the no. of stator in rotor in induction motor????
Who we calculate the generator NGR resistant, generator voltage 11 KV ?
what is residual current....
why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
7 Answers HCIL, Jindal, Siemens,
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
3.7 kw motor ,how much sq mm cabel want to bare this motor load
Why transformer neutral is earthed
How is the percentage impedence of a transformer fixed at design stage???
what is polarity in ac system? and how do identified?
What are the various methods for effecive earthing in a factory in a rocky terrain, where soil resistivity is extraordinarily high? The usual method of 3 m deep earth pits is not serving the purpose.
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side