what is the procedure for three phase motor differential
relay testing
can it do with single phase test kit?



what is the procedure for three phase motor differential relay testing can it do with single pha..

Answer / santosh kawade

Three phase motor differential relay testing can be done
with single phase test kit.

There are two type of relay testings:
1) Primary injection : In this testing entire system
(including relay, control wiring and power wiring get
checked),
2) Secondary injection : In this testing generally we check
relay only.

By using single phase test kit:
1) Primary injection :
a) Carryout shorting of all three phases of motor winding
by using short link for individual phases seperately.
b) Inject current by using current injection device (for
inzone and outzone fault)
3) Check stability of relay for outzone fault and operation
of relay for inzone fault.

2) Secondary injection :
Directly inject fault current in relay terminal and check
proper operation of relay.

Santosh Kawade
9224 69 3116

Is This Answer Correct ?    6 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate u.p.s load parsentage plz give me formula

1 Answers  


advantages & disadvantages of Lagging and leading power factor .

0 Answers   KMSC,


Benifits of 3ph 4 wire metering over 3ph 3 wire

0 Answers  


When batteries are connected in series the voltage increases but the current remains unchanged, how can this be? When you consider ohm's law. i.e. If voltage increases, current increases, providing resistance remains the same.

10 Answers  


whytransformers rating in KVA?

3 Answers   Chettinad,






Why is a thicker conductor necessary to carry a current in A.C.as compared to D.C. ?

1 Answers  


will aqatic animal die if we ground the wire of three phase instead of grounding to earth

2 Answers  


How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side

0 Answers  


What is required of exietation to the alternater.

4 Answers  


induction 3 phase motor terminal connection

0 Answers  


Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue

1 Answers  


what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks

0 Answers   ABC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)