what is the procedure for three phase motor differential
relay testing
can it do with single phase test kit?
Answer / santosh kawade
Three phase motor differential relay testing can be done
with single phase test kit.
There are two type of relay testings:
1) Primary injection : In this testing entire system
(including relay, control wiring and power wiring get
checked),
2) Secondary injection : In this testing generally we check
relay only.
By using single phase test kit:
1) Primary injection :
a) Carryout shorting of all three phases of motor winding
by using short link for individual phases seperately.
b) Inject current by using current injection device (for
inzone and outzone fault)
3) Check stability of relay for outzone fault and operation
of relay for inzone fault.
2) Secondary injection :
Directly inject fault current in relay terminal and check
proper operation of relay.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 6 Yes | 2 No |
How to calculate u.p.s load parsentage plz give me formula
advantages & disadvantages of Lagging and leading power factor .
Benifits of 3ph 4 wire metering over 3ph 3 wire
When batteries are connected in series the voltage increases but the current remains unchanged, how can this be? When you consider ohm's law. i.e. If voltage increases, current increases, providing resistance remains the same.
whytransformers rating in KVA?
Why is a thicker conductor necessary to carry a current in A.C.as compared to D.C. ?
will aqatic animal die if we ground the wire of three phase instead of grounding to earth
How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side
What is required of exietation to the alternater.
induction 3 phase motor terminal connection
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks