Answer / santosh kawade
Three phase motor differential relay testing can be done
with single phase test kit.
There are two type of relay testings:
1) Primary injection : In this testing entire system
(including relay, control wiring and power wiring get
checked),
2) Secondary injection : In this testing generally we check
relay only.
By using single phase test kit:
1) Primary injection :
a) Carryout shorting of all three phases of motor winding
by using short link for individual phases seperately.
b) Inject current by using current injection device (for
inzone and outzone fault)
3) Check stability of relay for outzone fault and operation
of relay for inzone fault.
2) Secondary injection :
Directly inject fault current in relay terminal and check
proper operation of relay.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 6 Yes | 2 No |
can you explain the rms value in simple words....
why the air gap is necessary in the transformer core
Can we use Motor protection CB while we use the VFD for Speed control?? if not means please tell the reason!!!
can anybody find out the result. I am lil bit confused about my equation.
Explain Random and Deterministic signals?
Why the transformers making noise?
hai every bodi please let me know the test procedure for lightning arresters.
Why rotating machines are not allowed to run near critical speed region?
DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED R VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV
We know that primary transmission is done to reduce current so that i^2*r loss could be minimised but according to ohm's law v is directly proportional to i,which indirectly means higher potential difference means larger current?so how the current is minimised in high power transmission line??
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)