in power station power measuring unit is KW but in
transformer is KVA why?
Answers were Sorted based on User's Feedback
Answer / dipak patil
the tf cu losses are proportion to current and irone or no-
load losses are propotional to voltage rating of
transformer. Since losses once available it is essy to
calculate transformer efficiency. Hence tf rating is given
in KVA insted of KW
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / engr. sumair mir
p.f=kw/kva .... T/f rating is in kva bcoz ,
1- Power factor of the load is not known.....
2- T/F losses depends upon cu- losses(due to current) and
core losses(due to voltage).
due to these resons t/f ratings are in kva.
while for motors and other machines the rating will be in kw
becoz their p.f is known(ranging from .2 to .8 during light
load and peak load period)...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srikanta
generally ratings of electrical machines are depends open losses and power factor.
in case of transformer copper loss depend on current and iron loss on voltage but independent of load power factor,hence it's rating is KVA rather than KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahmood al-ali
1- Any transformer includes core losses and copper losses
2- Core losses are based on input voltage
3- Copper losses are based on current flowing through winding
4- Therefor, total losses are based on voltage in addition to current but not power factor.
Thus, the rating of transformer is done in KVA not in KW
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the concept of star delta starter?
Why grables are put in substation?
what is automatic voltage regulator?we can control the vlotage by using fuzzy controller in matlab?why we go for fuzzy?
Explain Need of a starter in a dc motor.? Also explain any two starting and speed control method of dc motor?
Is 2000kva stabilizer suitable for 1h.p split air conditional
What is the differance between 2 dc motors of armature voltage 660 v and 440 v?
What is the difference b/w RMU & substation
what is excitation/
0 Answers ABB, Tata Steel Limited,
What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?
Is it required to use Automatic transfer Switch in L&T panel board if we use AMF panel with DG set? How the single line diagram will be? Please forward the material to sreenu_207@yahoo.co.in
define bilateral network and unilateral network? give an example.
what is ASCR cable and where we use it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)