in power station power measuring unit is KW but in
transformer is KVA why?
Answers were Sorted based on User's Feedback
Answer / dipak patil
the tf cu losses are proportion to current and irone or no-
load losses are propotional to voltage rating of
transformer. Since losses once available it is essy to
calculate transformer efficiency. Hence tf rating is given
in KVA insted of KW
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / engr. sumair mir
p.f=kw/kva .... T/f rating is in kva bcoz ,
1- Power factor of the load is not known.....
2- T/F losses depends upon cu- losses(due to current) and
core losses(due to voltage).
due to these resons t/f ratings are in kva.
while for motors and other machines the rating will be in kw
becoz their p.f is known(ranging from .2 to .8 during light
load and peak load period)...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srikanta
generally ratings of electrical machines are depends open losses and power factor.
in case of transformer copper loss depend on current and iron loss on voltage but independent of load power factor,hence it's rating is KVA rather than KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahmood al-ali
1- Any transformer includes core losses and copper losses
2- Core losses are based on input voltage
3- Copper losses are based on current flowing through winding
4- Therefor, total losses are based on voltage in addition to current but not power factor.
Thus, the rating of transformer is done in KVA not in KW
| Is This Answer Correct ? | 1 Yes | 0 No |
induction 3 phase motor terminal connection
How to know vacuum in vacuum cylinder of breaker in working condition
Hi friends, i m electrical engineer i want a cdr for migration purpose so anybody have information about this then send me on jayesh_ee88@yahoo.com.please try to me
in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
What is meant by SMPS how it working ... and where it used
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
WHAT IS SYNCHRONISING?
What Factors should we consider while synchronizing two DG Sets?
what exactly commisioning work does in electrical site work... LT side?..
Why Transformer does not work in DC ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)