I have one DP transmitter of range 0-500mmWC i have to
calculate its range in M3/hr for flow measurement so whats
the formula.
Answers were Sorted based on User's Feedback
You first need to have a flow element like a orifice plate
installed in order to get a differential pressure across the
orifice. You then need to measure this differential pressure
with the differential pressure transmitter or a u-tube or
two pressure gauges at various flow rates. If this is not
possible the orifice plate manufacturer will give you the
minimum and max diff pressure across the orifice plate for
various flow rates and liquids. You should already have the
pipe size, the orifice plate details and the liquid you will
use in this application.
Once you have this minimum and maximum diff pressures for
the minimum and max flow rates you can see on the
transmitter range if it will be big enough to measure these
diff pressures. The signal can be send from the transmitter
directly to the DCS and the squire roof extraction can be
done there or you can do the SQ extraction on the
transmitter itself by modifying it's configuration to
measure flow.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / kannan.r
range of dp tx and range of output is entirely different.
first of all to measure flow, we need primary elements like
ventury tube, flow nozzle, annubar which will restrict the
flow and so that dp will create.
from the manufacture of the primary element itself the
constant value should be noted. then only we can calculate
the flow using dp tx.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / umashankar soni
DP transmitter are used for flow measurement in combination
with flow obstructing devices such as
venturi,orifice,nozzle or aerofoil,which have tested
characteristics i.e. pressure drop across them for a
perticular flow.
This characteristic is then used with DP transmitter to
measure flow.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / sarma
simply measure dp at max flow. caliberate dptx to that
value. select output sqrt in dptx. if its out of range of
dptx. adjust orifice and try.
| Is This Answer Correct ? | 1 Yes | 2 No |
who discoverd ohms law?
What is wet leg condition and why is it used?
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
what is the process to make control schematic ?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
Why mmwc unit is used?
What is the Differance between Graphics And SCADA Graphics? SCADA Graphics have less access?
what is easiest way to read STL language in PLC?
if found error in magnetic flow meter?how can we adjust?
2 Answers ANI Instruments, Techint,
if we mount flow tube in arrow direction then flow comes in negative & if we mount it another direction then flow comes positive,So what will be the problem
hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank). can i use T/C or not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)