While testing the 33KV Busbar by using Hipot kit, what
should be the test
voltage we have to apply?
Answers were Sorted based on User's Feedback
Answer / dharmaraj
you apply voltage 80% factory testing.......
if example factory testing 70kv means
you apply 70*0.8 = 56kv. for 33kv busbar........